Discuss 32A MCB feeding 1.5mm & 2.5mm T&E cables via 30A terminal block in the UK Electrical Forum area at ElectriciansForums.net
Quickie - Would you say this is ok?
32A MCB feeding 6mm T&E which is then connected to a 2.5mm T&E & 1.5mm T&E cable via a 30A terminal block in plastic terminal block housing buried in stud wall.
The 2.5mm feeds a 3kW immersion heater with 13A SFU at the heater end.
The 1.5mm feeds gas boiler with 13A SFU at the boiler end.
Initially I thought the 1.5mm cable should not be fed with a 32A fuse but thinking about it - fault protection is provided by the 32A MCB & overload protection is provided by the 13A SFU at the end of the circuit rather than the beginning. Just doesn't seem good practice to feed a 1.5 & 2.5mm cable from a single 6mm cable protected by 32A but is it ok?
Not ideal to have boiler & water heater fed off same supply.
Fuse in switched fused spur to water heater is on the limiter - non fused switched unit would be better?
Connection should be maintenance free.
Should the connection be rated for design current or be equal to or greater than the fuse (in this case 32A)?
Many Thanks
Chris
Many Thanks
Chris
In a few words, no this is not an ideal situation. In my opinion.
The fcu does not provide fault protection to the cable but it does limit current flow. The cpc of the cable will need to carry fault current required for the 32A device to trip without suffering thermal damage.
Noticed this whilst carrying out other work in the dwelling, reduced the mcb to 6A & removed heater from circuit as temporary, writing customer a report so he can call back plumber/electrician to rectify new install.
Thanks for all your replies.
For brain exercise -
Using eqn in 543.1.3 with k=115, I get that 1 mm will support approx 360A for 100ms without damage. So if Zs is more than approx 0.54 Ohms but less than 1.1 Ohms it should work to disconnect from a B32. If circuit Zs is lower, then the 1.5mm cable with 1mm CPC will be heat damaged to clear a fault.
Appreciate it if anyone would like to check this?
So it was a Plumber that butchered the wiring in the first place was it?
Sounds like the 6mm supply cable for a cooker has been reutilised for other things.
I wonder what the cooker is connected to now? Nearest light switch?
No, Pete.... it was a plumber slash electrician. One of those highly double trained tradesmen we should be envious of
I see now it all make sense, bit like connecting the gas cooker to the 15 mm water main, done by a Plumber/Electrician/Gas Safe Engineer.
Very helpful! My comment would be that the MCB would likely be specified to trip quicker than 100ms, although good luck reading that off the graph!
My other comment is that Zs at the end of the 1.5mm is not the right thing to measure, it's the Zs at the point where the csa reduces to 1.5mm.
Zs should be measured at the furthest point, the supply terminals of the fcus.
Agree but for adiabatic the relevant impedence is the lowest case not the highest as it would be for disconnection time. Because there could be a fault anywhere on the cable and it would be worse case closer to the origin.
So closest. Not sure what it's called, not Zdb in this case as it's half way! Zr for reduction in csa maybe.
The only exception would be where the cable in question didn't need fault protection along its entire length, which i think is unlikely in this case.
Not sure why you are disagreeing, Zs is measured at the furthest point at the supply terminals of the fcus.
Yes sorry that's absolutely right but not relevant to the point, i was explaining about the"Z" at the point relevant to the adiabatic, of course you were right to correct me on my incorrect use of the term Zs. Sorry for confusing matters!
I have changed to creative as there's no button for "yes agree, but that's not the point in question"
Reply to 32A MCB feeding 1.5mm & 2.5mm T&E cables via 30A terminal block in the UK Electrical Forum area at ElectriciansForums.net
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's...
6K
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...