In the case of adjustable breakers which value goes in the column for protective device

i.e. if it a a 200a breaker and it has been tuned down to 180a?
 
You will then have to look at the graph of that type of breaker in BS7671, to get Zs values
 
As the 200A MCCB has been adjusted down to 180A that is the value to be taken. Are there any other adjustable parameters on this MCCB?? Always remember that adjustable MCCBs do not have a common trip value like MCB types. (B,C,D,) They are can be considered as ''one offs'' as there protection levels will vary according to the adjustment values being set on such breakers....
 
Last edited by a moderator:
You will then have to look at the graph of that type of breaker in BS7671, to get Zs values

If it is an MCCB to BS 60947-2, there are no max Zs values in BS 7671 for them. They can either be calculated or obtained from the manufacturer.
 
  • Like
Reactions: 1 person
If it is an MCCB to BS 60947-2, there are no max Zs values in BS 7671 for them. They can either be calculated or obtained from the manufacturer.

yep stand corrected, you can get the graphs from the manufacturers
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Adjustable breakers
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
brizospark,
Last reply from
Guest 004,
Replies
8
Views
2,649

Advert