Have you tried replacing the capacitors in the bollards ?
Many CFL bollards have power factor correction caps in them
 
I don't like the idea of the outside bollard supply going through someones flat
I worked on a flat where the supply to the flat next door passed through the flat I was working in.
My Boss at the time asked me what the two fuse carriers were?
 
.
 
If you say so I just wanted to know if the rcbo was essential for circuit protection.
 
As a lighting circuit, unless it supplies equipment in or passes through a location containing a bath or shower, you know as well as I do that it doesn’t require RCD protection.
 
If you do not manage to solve the problem after your next visit could you try these please (some of which have already been mentioned by others but included here as a neat summary):

a. Replace one of CFLs in the problem bollards with an incandescent lamps.

b. Replace both CFLs in the problem bollards with two incandescent lamps.

c. Try connecting only the problem bollards to the contactor if this is possible.

d. If the bollards are double pole switched by the contactor try single pole switching.

e. Use a temporary switch instead of the contactor to turn bollards on and off.

f. Use a switch instead of the photocell to turn the contactor on/off.

g. In the as wired set up connect an incandescent lamp across the contactor coil.

h. Measure the earth leakage current for all bollards, 4 bollards and if you can only the problem bollards.

i. Check the earthing of the bollards and the swa glands and nuts.

j. Do some ramp tests on the rcbo.

k. Check tightness of rcbo terminals. Is the functional earth connected?

l. Could you provide a sketch of the wiring including the contactor contacts and tells us the type of photocell and contactor.

m. Try fitting new CFLs to the problem bollards.

n. Inspect all connections for signs of tracking after the water ingress.

o. Temporarily swap over L and N to the bollards and see what happens when you turn on and off, first on the supply side then return to normal and then on the load side and then return to normal.

p. If there is another 6A RCBO temporarily use this to provide the supply.

q. Disconnect the L to the bollards on the load side of the contactor and switch contactor on/off, reconnect L and then do the same for the N to the bollards.

There is a better order to these but I leave you to sort that out.
 
Last edited:
Repeated post
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
MCR

Thread Information

Title
Any ideas, on this one..
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
48

Advert

Thread statistics

Created
nathz29,
Last reply from
marconi,
Replies
48
Views
5,015

Advert