Been asked to replace 4 Db's in a boat yard. Each to be fitted with 4 x 16A RCBO, 1 x 6A MCB and 100A Isolator. The sub main feed also has 4 x 16A RCBO and 1 x 6A MCB.
I see this as a Maximum current of 70A per DB, applying diversity could get this to 43A...
Now my problem is the main feed is via a C50 type B 30A RCCB, feeding the whole compound via a 10mm SWA!!! Table 4E4A shows maximum current of 71A.
Each DB daisy chained via 10mm SWA apart fromt the furthest which is 4mm SWA.
I guess that the whole compound has the ability to draw 215A after applying diversity for the DB's. This would mean replacing the main sub main feed with either a 70 or 95mm SWA. Also upgrading the swa trhoughout the chain of DB's. Also the main breaker to be upgraded to the maximum available to meet the cable spec.
Are my assumptions correct or is there another way of tackling this?
Your input is appreciated.........
I see this as a Maximum current of 70A per DB, applying diversity could get this to 43A...
Now my problem is the main feed is via a C50 type B 30A RCCB, feeding the whole compound via a 10mm SWA!!! Table 4E4A shows maximum current of 71A.
Each DB daisy chained via 10mm SWA apart fromt the furthest which is 4mm SWA.
I guess that the whole compound has the ability to draw 215A after applying diversity for the DB's. This would mean replacing the main sub main feed with either a 70 or 95mm SWA. Also upgrading the swa trhoughout the chain of DB's. Also the main breaker to be upgraded to the maximum available to meet the cable spec.
Are my assumptions correct or is there another way of tackling this?