Errr I am going to contact the guy in the letter. This is not a new supply they have been supplying the place for 30 years to my knowledge. But do they really expect me to calculate the load on maybe 70 DBs and then apply diversity to 66 different businesses??? Bit of a tall order unless I am missing something? And then divide by PF to to get Kva I suppose I think I am getting a bit of a head ache.
 
Can you upload the letter?
 
Oh yeh upload the file, that might help, funny thought I had nvm. Thanks for the answer @Wilko but as you know in the spirit of the forum it is here for FREE advice don't forget.:cool:
 

Attachments

save a shilling. just note meter reading now, and again after 1 week. simple maths concerning hours and leccy used.
 
What Amp is the supply?
Good question, I can't see into the boxes supplying the whole site. There is one main box and three subs to three different buildings, could take a look tomorrow to see if I can glean what is in there. May post a piccy. I am just trying to find the main supply in 300 pages of EICR may not be successful. Why is it you ask? to work out the Kva?
 
Brilliant!

If your business or organization is classified as Code 5 you should receive an electricity bill with itemized consumption figures at half-hour intervals. Usually the meter readings themselves are not included. The bill shows how much electricity is used at specific times as well as the cost of the electricity which is supplied during specific periods.

I don't know what happens if you go out of the scope of your authorised supply capacity..Do you get charged more for the KVA exceeded or is the authorised supply capacity averaged out over a period of time? If it's the former you want to be pretty accurate as you don't want to paying for more ASC than what you need but on the other hand you don't want to be using more than the ASC as the price per KVA is triple of what you are normally paying per KVA.
 
Good question, I can't see into the boxes supplying the whole site. There is one main box and three subs to three different buildings, could take a look tomorrow to see if I can glean what is in there. May post a piccy. I am just trying to find the main supply in 300 pages of EICR may not be successful. Why is it you ask? to work out the Kva?
Because if it's the lower end of the scale you can buy three phase energy monitors that you clamp round then you can access all the data via an app or online. A bit like the owl intuition energy monitors. By the sounds of it though it won't be any good to you. It's just a cheap way of load monitoring a supply but think the max is 200A per phase.
 
  • Like
Reactions: Vortigern
delete
 
Last edited:
  • Creative
Reactions: paul
If the meter has already been changed to a half hourly meter, you should be able to scroll through the different screens, one of which will be maximum demand.

Consider any winter or seasonal loads that may increase the maximum demand from what has already been measured.
 
more than the ASC as the price per KVA is triple of what you are normally paying per KVA.
Mhmm that sounds pretty serious and potentially expensive. I did not know that! Think I will have to have a serious chat with the man in the letter and get clued in to the implications cost wise for the client. Think this has just been sprung on the client and they haven't a clue as to what it is or what is being asked hence handed to me another clueless person in the chain of human incompetence. (NOT!)
 
  • Like
Reactions: Leesparkykent

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Calculate this. Just got this letter emailed to me...
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
The Ghost,
Last reply from
The Ghost,
Replies
19
Views
2,452

Advert