ok here i go :

For deign current : 36.1 A

In : 40A
...................

Ok..... here goes...

Ca : 35 oc...... : factor of 0.94....table 4b1 ?
Cg : 0.82........table 4C1 ???

so ...It = 50.8 A ...????

Im lost as to where i go from here....

I can do the volt drop calc....but i cant suss how to find the correct table for the cable selection ?

Thanks
 
you set sum out for me and paste orig question in too. thank you if you could aint done 3phase before

The question is in post #49
 
The question is about a 25KW 400V heater.
 
Ib -

Ib = Power / SQUARE ROOT of three x Uo = 36.1 A

In = Greater than Ib = 40A breaker

It : = In / Cg = 40 / 0.82 (table 4c1) ......It = 48.78 A

(these values have changed)

Cable : 4mm cable (Table 4G1A , column 9) ?????????????????
 
If your talking about load balancing over phases.....then....Yeah...kind of...but that would be in the inititial design of the heater itself......not considered during the heater installation...

Seeing as it a three phase supply...You consider that the load in q has already been balanced by the Maker of it.

Installers may need to consider balancing when installing single phase items...into a premesis that uses/ are provided by three phases...( ie,, three single phase (identical heaters) would be installed on a phase each ?


Correct me on this if im wrong though guys..
 
Ib = Power / SQUARE ROOT of three x Uo = 36.1 A

is that per phase?

The 36.1A figure is the design current for each line (L1, L2, L3) it is not a total value that is then shared between 3 cables if that is what you are asking:)

edit : you have to be a little careful with terminology because the phase current (Ip) only equals the line current (Il) when connected in star. If in delta, as it would most likely be in a motor, then Il = √3* Ip

When designing for cable size it is just the line current that you are interested in.

A complex subject (which i am rapidly forgetting:eek:) but just to be aware that phase current and line current are slightly different and are not always the same value.:)
 
Last edited by a moderator:
The 36.1A figure is the design current for each line (L1, L2, L3) it is not a total value that is then shared between 3 cables if that is what you are asking:)

edit : you have to be a little careful with terminology because the phase current (Ip) only equals the line current (Il) when connected in star. If in delta, as it would most likely be in a motor, then Il = √3* Ip

When designing for cable size it is just the line current that you are interested in.

A complex subject (which i am rapidly forgetting:eek:) but just to be aware that phase current and line current are slightly different and are not always the same value.:)

Much better explanation than mine...:)
 

Reply to Calculating volt drop, cable selection and mcb selection on an 3kw motor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock