- Feb 23, 2011
- 2,879
- 1
- 2,843
- 10,456,798
- If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
- United Kingdom
- What type of forum member are you?
- Practising Electrician (Qualified - Domestic or Commercial etc)
Hi all.
A local caravan site has asked me to test their RCD's. I popped in to speak to them about what they wanted and had a quick nosey around with a view to returning and undertaking the work.
The 32 electric hook-ups are fed via a 3 phase system which splits into 3 circuits. Each circuit is protected by a 100 mA RCCB, I think these are time delayed. Then at the hookup point each unit has 2 16A MCBs and they share a 30mA RCD unit as per Reg 415.1.1. (I note 708.553.1.12 and .13 says that each socket outlet shall have its own MCB and RCD etc).
The earthing system is definitely PME - I've spoken to the DNO engineer that installed it
When I did a quick test on a RCD at the hook-up it didn't trip out at 1/2 In but did at 1xIn and both parts of the waveform (o and 180 degrees). However when I tested at 5xIn my Megger kept reading back >50V. Does anyone have any idea why this might be? I tried switching over to the time delay setting but this had no effect, and as I say, they are standard 30mA RCD units. I tested several just to make sure it wasn't a dodgy one off.
I have a sneaky suspicion that there is no additional earth to the hook-up points and the manager thinks this might be the case too. Where the main incoming cable comes into the distribution box there is a separate 16 mm earth cable next to it running out into a soil pipe and into the ground. The DNO has a vague memory that originally an earth plate/rod was put in by a spark, but can't recall how long ago. The campsite manager is really helpful, but has only been there 3 years and there are no site records to show what has been done in the past. The owner has little interest and no clue either. (Incidentally the manager dug a test hole for me and we found the SWA cable serving the pitches barely at 30 cm with no additional physical protection/ warning tape or anything).
Sorry to sound ignorant but can I test this mysterious 16 mm cable by carrying out an earth fault loop impedance test as per GN3 page 17 to see if there is a means of TT earthing for these hook-ups? I have a Megger 1552 but no other specialist earth electrode test equipment?
Does anyone know how long earth rods/plates last for in the ground (sandy soil)? I'm just wondering if the site had a TT earth and it has corroded away and now not viable?
They also have 6 statics on site (3 belong to the caravan site and 3 are privately owned), that are fed from a different source (single phase) but also PME). The caravans are not far from the distribution board and on testing the RCD's either the Hook-up points or the main board RCCB's are tripping out at all ranges. However there is no time delay on these units and when testing it is somewhat a game of 'russian roulette' as to whether the hook-up RCD or the main board RCCB will trip out! Obviously this needs sorting out, but again the individual vans need their own TT earth? Is there any obligation upon me to notify the van owners that their vans are not correctly earthed and thus potentially dangerous under fault conditions? I have no way off obtaining the owners contact details unless the manager/owner wishes to advise me?
Any comments/observations would be gratefully received.