Hi Everyone

Had to replace an old Re-wirable fuse board last week in a small industrial unit, replaced with a split load board, originally had the compressor wired into the RCD protected side and everytime the compressor started it tripped out the RCD.

I have since moved it to the other non rcd protected side & it works fine. The compressor is protected by a 32A MCB has two motors which start with a time delay (I.E. one motor starts & runs and then the other) to prevent overload. I measured the start current to be 38A and the current when running is 23A.

I know the compressor does not need RCD protection, Just wondered why the RCD trips?

Thank you
 
I know it's not an RCBO (or is it?) but can RCDs trip in overcurrent situation?
Presumably a time delay circuit of contactors is used to control the motors. Is this wired up correctly (N to E fault on contactor circuit possibly?) Have you put a clamp round the earth to measure the leakage?
 
Hi

Thanks for the reply no I haven't put clamp around earth that's a good idea. I also didn't think an rcd should trip on overload. Unfortunately I didn't get time to test contactors etc.
 
Do you have another RCD you can substitute - thinking possible dodgy (in overcurrent) RCD. I take it the MCB remains closed when the RCD trips.
It may be possible initial contactor is shorted to earth so is then operating (but under fault conditions) and the fault is then taken out of circuit by timer action before the fault becomes apparent. Total guess this - only you can tell what the fault really is. Do let us know.
 

Reply to Compressor Trips RCD in the Canada area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock