It’shere to Stay [ SPD ] 2012
Section 443 – Simple Risk Assessment ]
Thefollowing are different consequential levels of protection:
(i) . Consequences relatedto human life, e.g. safety services, medicalequipment in hospitals
(ii). Consequences relatedto public services, e.g. loss of public services, IT centres, museums
(iii). Consequences to commercial or industry activity,e.g. hotels, banks, industries, commercial markets,farms
(iv) . Consequences togroups of individuals, e.g. large residential buildings, churches, offices,schools
(v) . Consequences to individuals, e.g. small ormedium residential buildings, small offices.
For levels of consequences(i) to (iii) protectionagainst overvoltage shall be provided.
IsProtection Required – Section 443 / BS- EN -62305
( Yes ) - Risk of direct lighting to or near structure .BS-EN-62305 : or Lighting protection system installed . ? 443.1.1.
□ Lightning current [ Type 1 SPD ] or combined [ Type 1 + 2 SPD ] on main switch board to prevent dangerous flashover ( 534.2.1 )
Overheadline supplying the building at risk of direct strike – see BS EN-62305 (443.1.1)
( Yes ) - Overheadline supplying the building at risk of direct strike : BS-EN-62305 . 443.1.1.
[ Alternativesimplified risk assessment: 443.2.4. ]
Installation presents higher risk (e.g. fire) or requires higherreliability (443.2.2 Note) - see BS EN-62305
[ Alternativesimplified risk assessment: 443.2.4. ]
□ Protection against overvoltages not required ( 443.2.1, : 443.2.2 ) if equipment impulse withstand voltage toTable 44.3
Installationpresents higher risk (e.g. fire) or requires higher reliability ( 443.2.2Note ) - see BS EN-62305
Consequences related to human life? For example safety/medical equipment (443.2.4)
[ simplifiedrisk assessment : 443.2.4. ]
Coordinatedset of overvoltage SPDs for equipment protection e.g. Type 2 or Type 2+ 3 for distribution boards feeding sensitiveelectronic equipment (534.2.6)
□ Protection against overvoltages not required if equipment withstandvoltage to Table 44.3
Consequencesrelating to groups of individuals or individuals - for example residential buildings (443.2.4)
Consequencesrelated to loss of public service ? For example IT centres, museums (443.2.4)
Consequences related to loss of commercial/industry activity? For example hotels, banks, farms (443.2.4)
□ Check if data, signal and telecom lines require protection (443.1.1, 534.2.1)