We have a control panel that has a few fan motors (3phase) and two heaters ( 3 phase) and single phase loads to valve actuators. My question is regarding the sizing of the feeder cable to this control panel. Do we work out all the currents individually and then add them and treat this as a "lump sum" to size the feeder cable and its associated protection.
Thanks very much
This control panel should be CE marked, and thus must have a total load stamped somewhere on it.
If it doesn't whoever has sold it has broken the law, and whoever now has it, if put in use will also be breaking the law.
On a technical aspect, adding the FLC of everything in the panel is a safe way of making sure the supply should big enough, however, what if all the motors are designed to start at once? Are they interlocked so only one motor can run at a time, if the latter is the case adding FLC will end up with an overrated supply and cost more than necessary.
If there are no drawings and no specifications for the equipment then you are in a bit of a pickle for doing the design (?) . Surely all the motors have a plate?
Yes I think it was marked but it's difficult to read now. Some of the equipment is for heating and some for cooling so these will not be on at the same time. What I am thinking is worse case and so taking it to be everything on at once , so for this approximation for the feeder cable we can take flc of all equipment and treat it as one load and then as more info becomes available we can factor in diversity etc ?
Reply to Control panel feeder cable sizing in the Industrial Electricians' Talk area at ElectriciansForums.net
Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...