If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Hi guys, I've been given the task of installing a 32A commando socket w/ isolator, which will have a 27A oven plugged into it. It will be on a C32 30mA RCBO. The cable from the oven is 4mm which will have the 32a commando plug fitted to it.

My question is, should I wire the 32A commando socket in 4mm or 6mm? The cable run isn't very long so voltage drop won't be an issue.
 
Hi guys, I've been given the task of installing a 32A commando socket w/ isolator, which will have a 27A oven plugged into it. It will be on a C32 30mA RCBO. The cable from the oven is 4mm which will have the 32a commando plug fitted to it.

My question is, should I wire the 32A commando socket in 4mm or 6mm? The cable run isn't very long so voltage drop won't be an issue.
Installation method
Length of run
What do your calculations tell you
 
Cable run: 12M
Installation method: Plastic conduit.
 
you using singles? any diversity applicable to the cooker?
 
Going to use multicore in cable tray to an adaptable box then singles down in conduit.
 
then base your calcs on the multicore cable as that will probably have the lowest ccc.
 
I work it out as 6mm
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Zdb

~
Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Cooker circuit (cable size?)
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Zdb,
Last reply from
davesparks,
Replies
7
Views
5,725

Advert