whazza22

Hi all

Is there anywhere in the regs about using crimps in a consumer unit?

I have a 32a ring circuit and would like to add some additional sockets in a room where the consumer unit is. There are no local sockets nearby and no spare ways in consumer unit. Therefore, I was planning on extending the existing ring circuit by crimping one leg with a new leg then continue the ring back to the mcb (if you get my drift)

Is this acceptable?
 
Dont think thier is a reg that stops you doing it how else would you edxtend a cable that broke but if you need to move a cu it may be worth looking at din rail by line
 
Yep no problem with that however make sure you double check that the crimps are sound and use a proper crimping tool. I personally only ever use them as a last resort and not that keen on wagos either. I now await the barrage of people cussing me for saying this.
 
Yep no problem with that however make sure you double check that the crimps are sound and use a proper crimping tool. I personally only ever use them as a last resort and not that keen on wagos either. I now await the barrage of people cussing me for saying this.

I was really dubious of wagos to start mate, but i gotta say, now i couldnt live without them, and they have zero failure rate, and a damn sight quicker.
 
Yes perfectly acceptable, I'd say a good job too better than connector block

Lets hope it's a ratchet crimping tool for starters. Using crimps, straight through or eyelet or whatever type have always been good practice on stranded or flexible cores however on solid cores a screwed terminal is the way forward.
 
Screwed terminals are so "last year" have used wagos, ideal connectors and hellerman, not had 1 problem that I know of, connector blocks are on there way out, even crimps for a one in one out Connection are better than connector block
 
Screwless connectors haven't been around long enough in domestic circuits to be able to say they are faultless.

Screwless connectors have however been around in commercial / industrial installations for a long time and they do fail.
 
As brought up many times on here regarding crimpng ... solid cores should not be crimped with standard lugs and ratchet crimp they are designed for stranded cables, the ratchet crimp most people have is the wrong one and also you will have to source the correct crimps to as your standard crimps also are not for solid, so either use a dinrail mount connectors in appropriate enclosures or use I-Line / Wagos etc thats of course if you dont want to use bog standard connectors.
 
As brought up many times on here regarding crimpng ... solid cores should not be crimped with standard lugs and ratchet crimp they are designed for stranded cables, the ratchet crimp most people have is the wrong one and also you will have to source the correct crimps to as your standard crimps also are not for solid, so either use a dinrail mount connectors in appropriate enclosures or use I-Line / Wagos etc thats of course if you dont want to use bog standard connectors.
I like this answer that was what I was getting at with the question on MICC, well put, also whatever anyone else thinks I would still feel happier with screwed connections.
 
Getting back to the original question why don't you pull one leg of the ring out of the CU terminate it into a enclosed JB extend the ring to your new sockets and back to the CU all done and dusted and a good job at that.
 
i would rather use waggo,but if the connection is accessable[ie:inside cu or in cu enclosure]/ in jb then terminal strip or 3 terminal jb should be ok
 
Well it seems ive been doing it wrong for the past 10 years, along with loads of other people ive worked with. as ive always used crimps on solid core cables.
 
Well it seems ive been doing it wrong for the past 10 years, along with loads of other people ive worked with. as ive always used crimps on solid core cables.
Me too, oops! Always thought crimps were for solid cables too always give them a good tug and to my knowledge never seen a burnt out crimp, but I have been proven wrong many times - mostly by the wife though
 
Solid core crimping in banned in most industries like rail, NASA, Aviation etc etc but stranded or allowed it kind of spells it out for you as its been proven time and time again to be an unreliable crimping method...

And here's the reason... when you crimp a stranded cable with correct ratchet crimper it shapes the crimp in a manor that it holds its structural integrity and give good surface area contact, with stranded this is easily achieved as the crimping action shapes the strands into a tight formation and because they are loose they adapt to the crimp shape.
Now a solid core doesn't mold into the crimp shape and create a situe where the crimp deforms around it which can't guarantee the crimps structural integrity and also surface contact can sometimes be at two points only the top and the bottom with pockets around the core.
The final issue is flexing of cables if a standed cable is moved and wiggled all the energy is absorbed in the flexing of the strands where-as solid core tranmits a large percentage of the energy into the crimp joint where it becomes prone to loosening even after just a few occasions as this is also coupled with a deformed crimp joint.
 
I think anyone who's been involved in any major industrial electrical contracts would know this about crimps, but people who have spent all their working lives on house bashing wouldn't lol
 
Just shows even after 10 years people are still learning, nobody knows it all that's what we're all here for to share things we know
 
Back to the OP, what load is there going to be on the new sockets? If its small I'd do a spur from the CU to a FCU, then to the sockets. Far better IMHO
 
crimped lots of cables on house bashing, never had any problem, good ratchet crimper and insulated blue crimps do the job for 2.5 cable. its not nasa, those cables wont fly to space.
you can stick them in some wago too.
 
Where would you use crimps house bashing?
crimped lots of cables on house bashing, never had any problem, good ratchet crimper and insulated blue crimps do the job for 2.5 cable. its not nasa, those cables wont fly to space.
you can stick them in some wago too.
 
Take one leg out and put to a socket next to consumer unit then on to other sockets then return to cu if you don't want any joints, be it crimps, connector blocks or other methods....nice easy test point aswell for Rcd tripping times in future cus that's all it would get used for lol
 
Never had the problems that have been mentioned above, crimping solid core cables. The only bad crimps i've seen using a good crimping tool and good crimps, have been down to operator error!!
Though i don't like the PVC insulated crimps, i prefer the heat shrink type, and better still bare crimps, with heat shrink tube covering!!
 
On virtually every project i've been involved with, on final distribution boards every termination into protective devices, relays, contactors and the like within those distribution boards have ALL been crimped terminations of one type or another!!

As far as i've seen, rail signaling cables and the like are basically all stranded cables anyway, as are cabling and wiring on the trains themselves, The same as your typical car, stranded wiring is used throughout for obvious reasons. Your typical electrical installation isn't subject to continuous vibration or anything like it, so why try and impose rules based on criteria that it won't be subject too!!


As for the wiggling free thing, you can say exactly the same thing about every screwed wire/cable connection ever made, ...So do we ban these now??


Let commonsense rule for a change!! lol!!
 
I see your reasoning E54 but consider a bunch crimps within a consumer unit YES! untouched and no vibration they may well serve there purpose but any following spark who makes additions, test or alterations and moves the cables cannot know or guarantee the integrity of the original joint hasnt been compromised simple saying it isnt subject to continuous vibration or anything is a poor argument to justify what amongst many industries has been deemed to be bad practice and a unreliable jointing method (refering to solid core crimping using standard ratchet and crimps).
Just because you may not of had or experienced any issues with this method does not justify it in a debate, all cable connection methods used throughout any industry has been scrutinised tested and examined to determine whether acceptable and crimping with standard ratchet and using standard crimps fails the test because of the reasons in my previous post -the solid core keeps shape while the crimp deforms around it which is not how the manufacturers designed it.. the crimp needs to take the shape its designed to do and the cable needs to mould to this crimp shape which isnt an issue when cores are stranded.

The reason why its a grey area in our industry is its been accepted that this isnt a wide spread practice as those who crimp often know it shouldn't be done and many alternatives exist, its just the case that your average domestic sparky tools up with a crimper and thinks its versatile and usable for all types of cable which had they done their research they will find it is not.

I was taught at college about the various crimping methods and tools we were shown blown up images of incorrect crimping methods and why and one showed a solid core and the crimp itself had fracture lines and contact free pockets around the core meaning surface area contact was minimal, i see often those argue against me saying they never had an isssue etc etc but with no other backing of the argument... if you want il try digging out my 25yr old college papers and forward the pics

Just an Edit to re-iterate we are discussing using the standard ratchet crimp and standard crimps here other forms of crimp are acceptabe on solid and are so designed i.e. data cables, telephone crimps etc
 
Last edited:
On this occaision i'm going to have to disagree with you darkwood. You make a good solidly crimped connection to a solid cored cable, sound as if it's a disaster waiting to happen, and i know the truth of the matter, is that it isn't! It'll still be there giving sterling service long after i've left this earth.

I defy anyone to wiggle or pull a solid core conductor out of a well made crimped connection (unless your King Kong..lol!!). If you can say the same for a screwed connection, i'd be very impressed!!

Having said that, i'm not keen at all on the popular coloured PVC crimps, to big and bulky and easily misaligned in the crimping tool jaws. My preference is bare crimps that are then over covered with heat shrink over the actual connection and an over all cover of heat-shrink (talking about Butt crimps here).

I can understand your reasoning if were talking about a moving/vibrating environment, but were not. ... Moving a cable within a DB/CU at a future date isn't going to degrade a crimped connection to a point of failure, this is also a non-starter for an argument against crimped connectors...
 
Last edited by a moderator:
Well on this occasion we will agree to disagree as i have alot of respect for your input on this forum but out of interest il set you a task of finding a picture of butt crimps or even ring lugs on the internet done on solid cable (without taking a pic yourself and cheating)...I found examples of poor crimps and bad practices but all are shown using stranded or fine wire ...out of the whole world wide web you'd have thought if it was so designed for solid there would be at least some examples of crimping it?
 
Well on this occasion we will agree to disagree as i have alot of respect for your input on this forum but out of interest il set you a task of finding a picture of butt crimps or even ring lugs on the internet done on solid cable (without taking a pic yourself and cheating)...I found examples of poor crimps and bad practices but all are shown using stranded or fine wire ...out of the whole world wide web you'd have thought if it was so designed for solid there would be at least some examples of crimping it?

Agreed, and also have a lot of respect for your inputs on the forum too...

I'm not going by what others have stated, or what has been printed etc. I'm basing all i have stated on this issue, on the literary hundreds of thousands of crimped terminations at final DB/CU boards among other areas, over numerous specified project contracts, over too many years to think about!! lol!!
 
Just relating back to those who express the crimps feel sound and cant be pulled apart i like to show a few examples... one good and one bad but both pass the strain test and this is why its a poor way to judge a crimp joint. PS i couldnt find a crimp joint on solid as manufacturers dont design butt crimps and lugs for this so examples of them are scarce.

. Good crimp.jpg . Bad crimp.jpg
 
Perhaps in China they do as they please with crimps lol just accept the fact you have been wrong all these years, please use the right crimp for the right job, the type of crimp that this threat started with as far as I could make out is the straight through insulated blue type, which is fine as long as it is used on stranded / flexible cores and in an enclosure. End of story
I'd stick with your ''screwed'' connectors they will surely out perform a ''crimped'' connection!! Well in your world anyway!! lol!!
 

Reply to Crimps in consumer unit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
775
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
325
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
795
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
762

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock