GraniteGuy

Don't know where it goes to (magnetic contact we think) but the Customer is happy to have that cable disabled. There are four wires - do I simply wrap all four together so the rest of the alarm can be switched on ?
 
You will need to identify what cores are used for the alarm and tamper circuits then join each of the cores together for the alarm and tamper circuits joining all four together will cause a fault which will stop the alarm arming. You could get an alarm JB and reconnect it would save time identifying what the cable does
If the magnetic contact is on the exit door the system may not set if it is programmed for final exit set and the door contact has been removed from the system
 
join the cables, colour for colour, if there is insufficient slack, the use 2 alarm JBs. If the alarm won't work, you'll be blamed.
 
Thanks. I tried a few different combination's and eventually figured out to wrap the blue and yellow together and the red and black together. Jobs a good un'
 

Reply to Cut through an alarm cable in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Can someone please guide me on this? I have virtually no experience of home alarm systems. The client has an alarm which had been fitted to her...
Replies
17
Views
1K
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
421
Hi all, I currently have a Pyronix Enforcer V10 Wireless alarm system. I have some shock/contacts on windows, doors, PIRs, and an external siren...
Replies
0
Views
763
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
734
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
4
Views
138

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock