Evening all ,
Called out to short circuit on cooker circuit assumed that cupboard fitted above isolater switch screwed through cable , disconnected at switch then dead tested back to board
Continuity l- cpc .22
l-n .16
n-cpc .22
Ir test l-n 999
l- cpc 999
n-cpc 999
All passed yet still shorted out any ideas plan to replace whole cable.
 
I would have thought the IR test would have shown any screw through the cable. There is nothing shorting within the isolator when you screw it back is there. Why don't you redo the IR test with the isolator connected.
 
I would have thought the IR test would have shown any screw through the cable. There is nothing shorting within the isolator when you screw it back is there. Why don't you redo the IR test with the isolator connected.
I thought IR test should have picked it up most confused that it did not , left cable free to air just choc blocks not connected at all thinking isolater problem still tripped mcb . must be cable pierced a fraction ?
 
Why have you decided the fault lies with this cable, there is more to the circuit than the cable to the isolator. Test it all.
 
Why have you decided the fault lies with this cable, there is more to the circuit than the cable to the isolator. Test it all.
What voltage did you do the IR testing at?
240 and 500 volts
What voltage did you do the IR testing at?
Why have you decided the fault lies with this cable, there is more to the circuit than the cable to the isolator. Test it all.
IR test at 240 500 volts , New cupboard fitted above isolater switch led me to think cable damaged from isolater back to board .
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
wawwick

Thread Information

Title
Dead test fail?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
ryan77,
Last reply from
AndyL,
Replies
27
Views
3,289

Advert

Back
Top