M
Mr.Black
Does anyone know or where to find the calculation you do to find a fault/break in a circuit that can't be physically traced.I'm sure i've seen it somewhere in one of my books but can't remember.
Cheers
If its a break then to find the fault you need a TDR (Time domain reflectometer), it basically sends a signal down the wire and at the break the signal gets 'reflected' back, based on the time it takes the signal to return, it can tell you how far down the cable the fault is.
If the fault is a dead short between cores then by doing a resistance measurement between the shorted cores and knowing the resistance of the conductor (based on CSA) per meter, you maybe able to gauge how far away the 'short' is. If the 'short' is not a 0 ohm short then you've got a problem!
If it is a dead short say on a radial caused by a nail connecting two of the conductors(if it is a ring disconnect one end) test resistance between conductors at CU and sockets - the position with the smallest reading is the closest. Identify the conductor size - and look up the resistance per metre in table 9A of the OSG for the size of the conductors involved. Divide that value into the lowest resistance reading and you have the distance of that reading from the fault.
Only works really well if you have a very good contact between conductors, but even if it is not perfect can still get you close to it.
Reply to Distance Calculation to find fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
My friend has got one of those robot lawnmowers that automatically goes out once a day and runs around the grass. There is a single core guide...
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Hi I'm trying to find if I have a fault in these to brakers of in the lines. The 32A braker leads as far as I know only to a junction box that use...