Jusk seeking affirmation really, still new to this world and want to make sure I'm not making silly errors.
1). 6mm2 3-core SWA over 20m @ 230V: 6.6mV x 16A x 20m = 2.048V
2). 10mm2 3-core SWA over 20m @ 230V: 3.8mV x 20A x 20m = 1.52V
3). 16mm2 4-core SWA over 5m @ 400V: 2.4mV x 63A x 5m = 0.756V
4). 25mm2 3-core SWA over 5m @ 400V: 1.5mV x 80A x 5m = 0.6V
I'm using the 3% rule, so +/- 6.9V @ 230V and +/- 12V @ 400V, is that the correct percentage to use for both?