1ManRiot

Jusk seeking affirmation really, still new to this world and want to make sure I'm not making silly errors.

1). 6mm2 3-core SWA over 20m @ 230V: 6.6mV x 16A x 20m = 2.048V

2). 10mm2 3-core SWA over 20m @ 230V: 3.8mV x 20A x 20m = 1.52V

3). 16mm2 4-core SWA over 5m @ 400V: 2.4mV x 63A x 5m = 0.756V

4). 25mm2 3-core SWA over 5m @ 400V: 1.5mV x 80A x 5m = 0.6V

I'm using the 3% rule, so +/- 6.9V @ 230V and +/- 12V @ 400V, is that the correct percentage to use for both?
 
3% is allowed for lighting. anything else, generally is 5%.
 
Just seeking affirmation really, still new to this world and want to make sure I'm not making silly errors.

1). 6mm2 3-core SWA over 20m @ 230V: 6.4mV x 16A x 20m = 2.048V: if 230V then only 2 live cores? so 7.3mV/A/m?

2). 10mm2 3-core SWA over 20m @ 230V: 3.8mV x 20A x 20m = 1.52V: if 230V then only 2 live cores? so 4.4mV/A/m?

3). 16mm2 4-core SWA over 5m @ 400V: 2.4mV x 63A x 5m = 0.756V OK

4). 25mm2 3-core SWA over 5m @ 400V: 1.5mV x 80A x 5m = 0.6V OK

I'm using the 3% rule, so +/- 6.9V @ 230V and +/- 12V @ 400V, is that the correct percentage to use for both?
Possible amendments above.
It looks like you are using maximum current rather than design current, design current would lower the values but they are well within so good to use worst case scenario.
 
Possible amendments above.
It looks like you are using maximum current rather than design current, design current would lower the values but they are well within so good to use worst case scenario.
Good call, that's the silly mistake I was making!

Yeah intentionally worked with the fuse values basically for worst case scenario- this is more an amendment and addition rather than a new design.
 

Reply to Double check my VD calcs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi folks, I'm installing a 3-ph 32A 60309 socket and just wanted to double check my design calcs are right... The circuit will be part of a 3-ph...
Replies
3
Views
2K
Excuse how long winded this is but want peoples opinion: :angel_smile::frown2: Doing a basic shed install but would just like people...
Replies
11
Views
2K
Octopus
O
J
I need to get a 3 phase 400v supply over to a unit with around 32amp per phase. The total length of the run is 108 meter fro source to consumer...
Replies
11
Views
1K
W
Hi guys, Looked over some previous posts and done some further reading, and attempted the calcs, just want to check that i am not miles off the...
Replies
8
Views
2K
wade88
W
T
Hi people. My first post on this forum - many thanks in advance for the commitment to it, hopefully I may be able to contribute as well. For...
Replies
5
Views
4K
Spazz
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock