The minimum CSA for a protective conductor that is not incorporated in a cable such as T&E is 2.5mm², if provided with mechanical protection, 4mm² if not provided with mechanical protection.
Regulation 543.1.1 ...
"If the protective conductor:
(iii) is not an integral part of a cable, or
(iv) is not formed by conduit, ducting or trunking, or
(v) is not contained in an enclosure formed by a wiring system,
the cross-sectional area shall not be less than 2.5mm² copper equivalent if protection against mechanical damage is provided, and 4mm² copper equivalent if mechanical protetion is not provided (see also Regulation 543.3.1)."
Not 100% sure what exactly an enclosure formed by a wiring system is?