Looking for some technical advice Regarding having EDF coming to connect a new Meter for a (3yr) Temporary TT System supply.

The connection was refused at first and he left a sheet with 2 points.

1. "earth rod" - (this has been sorted now) I've installed an earth rod with clamp and 16mm earth to the MET block.

2. "RCD REQD (Circuits)"


Now regarding point 2 - The main CCU has all RCBO's. But the CCU is contained in a separate box 2M's away. Im wondering if he didnt bother to look in here, or if he is wanting a main RCD between the meter and the CCU?


I was wondering if someone can guide me into make the setup perfect so that there is no risk of the guy form EDF leaving again.


A little detail into the diagram to help you visualize:

From the head there are unconnected meter tails to a henley block, and from the henley block to a 100A fused main switch. then from there to a connection box where the Tails will connect to the SWA. And from that SWA it goes undeground 2 meters to a wylex CCU with RCBO protection.

Thanks in advance
Tom
 
if the tails are not buried, no need for RCD. a bit more detail would help. along with a photo or 2.
 
hope it's not one of them thin 3ft. twigs. you need at least 2 5/8" coupled rods, preferably 3. go deep, as the actress said to the bishop.
 
You need Rcd protection for the sub main to the ccu, it sounds like to me anyway

I'd agree with that. Without an RCD at the supply end, you don't have any earth fault protection for your SWA (unless the TT rod has a VERY low Ra). The upfront RCD could be 100mA, S type. I'm sure someone will correct me if I'm wrong here.
 
Yea i have a 5/8" Rod. But do you think they will reject it if its only the one?

And what would people suggestions be to main RCD unit? just a standard standalone self unit after the fused main switch?
 

Reply to EDF coming to connect new meter at temporary site. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

If there isn't a 2-pole isolator there already, I usually get the client to arrange to get one fitted before I do a board change, either through...
Replies
20
Views
3K
I've just been sent this, not been there yet. At least 2 new circuits needed and things are a little.....tight...! Hager board is 10 modules and...
Replies
17
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock