- Reaction score
- 423
The problem can still occour with single phase, google the rcd handbook page 37 onwards
Discuss Fault finding query in the UK Electrical Forum area at ElectriciansForums.net
Again, HID lamps make a lot of noise and there may also be a faulty one which is breaking down when the ignitor goes off at turn on, spikes of several KV. Please read the notes I mentioned above, and split the load into several RCDs so one fault does not cause darkness.
Thanks guys, I was wondering what the leakage on the fittings would normally be. So if 2mA x 20 fittings = only 40mA so is well under the 210mA my rcd is tripping at on the ramp test.
So so probably a combination of old control gear and possible contactor issue. What about my rcd? I thought I should be changing it as its tripping well under 300mA?
Was the load disconnected when ramp testing the RCD?
Yes mate.
The BS requirements for RCDs states that the RCD should operate between 50% and 100% of its rated tripping current.
Reply to Fault finding query in the UK Electrical Forum area at ElectriciansForums.net