Hi,
I have one socket in my utility room, this socket is part of the down stairs ring main. I have taken a fused spur from this socket and ran two sockets of it, room is smaller than 12m squared, so 3 sockets is recommended for this size room, is that correct? I have used 2.5mm cable to run the two extra sockets. I am going too run a fridge of one of the new sockets, and use the other occasionally for a tumble dryer. The original socket which is in the ring main will run a washing machine, is this ok. I have City and guilds c2330, and could do with your advice on this matter.
Cheers.
 
Not ideal but if its protected by 13a fuse at spur its protected.. So zs test and just dont hope for overload.. But if that happens im sure you wont use everything at once
 
problem is a 13A fuse might not suffice the load your describing..

your best to extend the ring properly instead of spurring off

and you say you have CG2330 ??

what level are you at ? :mad:
 
What you are proposing is ok apart from load !! Its not something I would do, I would extend the ring. The two sockets would only be rated at 13A so in this case its a no sir
 
Its going to be on 32a breaker 8a on dryer washing machine 8 and fridge 4a max.. I think will be ok but im guessing. With no figures and
 
Hello, Thanks for all the advice. I will extend the ring so that the two sockets are incorporated into it, best be on the safe side. Busy at the moment doing level 3 2330. Will get some to inspect and test it though.
Cheers again for the good advice lads, as always. SAFTY FIRST, want to sleep at night.
 
You were going to run one 2.5mm from the ring socket,so it just as well be 2x2.5mm and crimp the cables at that socket to extend the ring
Do a continuity test on that ring before proceeding with the work

Remember installing electrics goes hand in hand with using the testers to verify that what you have installed is safe
None of us are fortune tellers,testing installs is essential
 
prefer to see RFC extended. use wagos in existing back box. if necessary, fit a deeper box.
 
wagos for me on solid conductors. seen too many crimps fail.
 

Reply to Fused Spur for two new sockets for utility room, taken from ring main. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
951
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
747
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
269

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock