Hi everyone
I've been out the business a long time and am rusty on regs. Perhaps someone can assist?

My son has an armoured cable fed from his house CU via a dedicated mcb to his detached garage.

This cable is connected to a 'Lewden' 'garage' CU consisting of a 6A mcb feeding two small flourescent light fittings and a 16A mcb feeding one double switched socket.

He uses several rechargeable drills/tools etc in his job and currently uses two 4-way extension leads to recharge everything.

I'm proposing installing four additional double switched sockets and returning to his garage CU to change the feed to a ring. I appreciate this means I need to change his 16A mcb to a 32 A mcb.

To save changing the 16A for a 32A, is it within the regs to simple add four more sockets i.e. have five in total on a single cable?
 
So what you're saying is you've never been in the business you're a DIYer that wishes for some advice.

Yes, you can add four more sockets. I'm sure those who do domestic work will correct me if I'm wrong here, but this work will be notifiable to building control, and will need a minor works certificate producing.

- Corrected by others, not notifiable if it stays as a radial circuit and is already RCD protected.
 
Last edited by a moderator:
The additional sockets would need RCD protection (take it's a domestic garage). If the circuit remains as a radial, it would not need a compliance cert.

As Rob said, what level of competence, expertise and test equipment do you have?
 
Yes you can add extra sockets to the 16A circuit, however the sockets require RCD protection.
No there is no requirement to notify.
Easiest way to provide RCD protection, would be to swap the 16A MCB for either a 16A or 20A RCBO.
 
To clarify:
I'm a timed served electrician who then qualified as an engineer. I've worked in the Merchant Navy as an Electrical Engineer and Nuclear Power Stations. This experience removes me from the DIYer status but have not worked in domestic situations since I was in my early twenties (50 years ago!) and am therefore not familiar with current IEE Regs.

My original question is to ascertain whether I'm acting within regulations (whether building or IEE) in simply adding four more sockets to his existing radial circuit or do I have to make the radial a ring circuit and change the 16A mcb to a 32A mcb.

Much appreciate any help.
 
To clarify:
I'm a timed served electrician who then qualified as an engineer. I've worked in the Merchant Navy as an Electrical Engineer and Nuclear Power Stations. This experience removes me from the DIYer status but have not worked in domestic situations since I was in my early twenties (50 years ago!) and am therefore not familiar with current IEE Regs.

My original question is to ascertain whether I'm acting within regulations (whether building or IEE) in simply adding four more sockets to his existing radial circuit or do I have to make the radial a ring circuit and change the 16A mcb to a 32A mcb.

Much appreciate any help.
You do not have to change from radial to ring.
You do not have to change the MCB from 16A to 32A.
What you do have to do, is provide RCD protection for the new sockets.
This can be by using RCD sockets, swapping the 16A MCB for an RCBO, installing an RCD before the garage CU or by providing RCD protection at the house.
 
To make any changes means that the changes you make must comply with current regulations Spinlondon has summarised this effectively.
It should be clarified that this RCD protection should be 30mA and that if there is already such protection further protection is not required.
You would also need to provide a minor electrical installation works certificate detailing the compliant results of your testing.
All this is assuming that the basic factors of the existing circuit are currently safely and compliantly installed.
Under building regulations in England, almost no matter what you do, if it is described in the above posts, it would not be notifiable work.
 
So why would a board change be notifiable? Essentially all you are doing is changing the OCPD a handful of times.
Not sure of the reasons, but in the case discussed only one circuit is being altered, looking at the "Wiring Matters article" changing a CU does not constitute any Minor Works, their words not mine,
 
You do not have to change from radial to ring.
You do not have to change the MCB from 16A to 32A.
What you do have to do, is provide RCD protection for the new sockets.
This can be by using RCD sockets, swapping the 16A MCB for an RCBO, installing an RCD before the garage CU or by providing RCD protection at the house.
Dare I ask what the OCPD is for the garage submain?

Dare I ask what the OCPD is for the garage submain?
I will check this out since I'm not sure whether it is from an OCPD in the house CU.
 
You do not have to change from radial to ring.
You do not have to change the MCB from 16A to 32A.
What you do have to do, is provide RCD protection for the new sockets.
This can be by using RCD sockets, swapping the 16A MCB for an RCBO, installing an RCD before the garage CU or by providing RCD protection at the house.

Thank you for all the above, it's much appreciated.
I'm going to extend the radial with four additional D/Skts.
After ascertaining whether the garage supply from the house is from an OCPD or the garage CU has its own inbuilt, I'll exchange the 16A mcb for a 16A RCBO.
The garage CU shows RCCB protected 63A 30mA. I will check this out but read this as being adequately protected?
 
Thank you for all the above, it's much appreciated.
I'm going to extend the radial with four additional D/Skts.
After ascertaining whether the garage supply from the house is from an OCPD or the garage CU has its own inbuilt, I'll exchange the 16A mcb for a 16A RCBO.
The garage CU shows RCCB protected 63A 30mA. I will check this out but read this as being adequately protected?
Dare I ask what size cable you will be using, and what method of installation, if the house CU has RCD protection and the Garage feed is coming from a cb on the RCD side of th CU (assuming it's not an amd 3CU) then all you need do is change the cb in the CU for a 20A, you don't want to go sticking RCDs Willy Nilly all over the shop, If as you mention the garage CU has an RCD then you will be covered. More than 1 RCD in the same circuit will only cause tripping problems.
 
In fairness to hightower there is certainly a train of thought that altering the protective device makes it no longer minor works (or suitable for a MEIWC) and that you are essentially creating a new circuit (although all/most of it has already been wired).
 
Old? The coals are permanently warm!
NICEIC never off the burner, simmering in the background.
In fairness to hightower there is certainly a train of thought that altering the protective device makes it no longer minor works (or suitable for a MEIWC) and that you are essentially creating a new circuit (although all/most of it has already been wired).
It's a difficult one this, although whilst I understand HT's thinking, it's still just an alteration, you could say you are creating a new circuit if you add, say 3 more twin sockets to a radial with just 1 original socket, I going to stick with MNWC, as an altered circuit, sorry HT.
 
I wish you lot would get all emotional when I talk out my ****, as I often do :)

I seem to recall I made a similar blunder last year, on this very subject. Which resulted in outright commendation & derision (you took the mick). But least I had the strong moral character (get used to looking a ----), and post the reply back from my scheme (document #15) o_O
 
I wish you lot would get all emotional when I talk out my ****, as I often do :)

I seem to recall I made a similar blunder last year, on this very subject. Which resulted in outright commendation & derision (you took the mick). But least I had the strong moral character (get used to looking a ****), and post the reply back from my scheme (document #15) o_O
When do you ever talk out of your backside?
 
Quite often I wake up in the morning Pete, particularly at weekends, and can't remember making the remarks in a post from the night before. :eek:

I reckon someone's hacked my account and making spurious remarks. I think that's 'wear' or all those bad grammars things come from, that sparksburntout picks me up on.
 
Last edited:
Quite often I wake up in the morning Pete, particularly at weekends, and can't remember making the remarks in a post from the night before. :eek:

I reckon someone's hacked my account and making spurious remarks. I think that's 'wear' or those bad grammars things come from, that sparksburntout picks me up on.
You're lucky, I sometimes can't remember what I said 5 minutes ago, who are you and what do you want?
 
xcuse my ignerrrence, but wat is a forum?
 
GN3 p110 gives an example of an MEIWC being used when replacing a circuit breaker with an RCBO of the same rating (as well as some lighting points being added to the circuit in the example). If I was changing the rating or type of the OCPD, I personally would use an EIC but I can see the argument for using a MEIWC. Converting a radial circuit to an RFC, I would definitely use an EIC.
 
GN3 p110 gives an example of an MEIWC being used when replacing a circuit breaker with an RCBO of the same rating (as well as some lighting points being added to the circuit in the example). If I was changing the rating or type of the OCPD, I personally would use an EIC but I can see the argument for using a MEIWC. Converting a radial circuit to an RFC, I would definitely use an EIC.
Why? you would be altering or adding to an existing circuit, making work for yourself there Steve, sorry but I disagree with your logic on the Radial to Ring scenario.
 
Why, why, why would any one bother with an EIC when a MWC would do............ are you mad.............
No comment. I plead the 5th amendment, or should that be the 3rd, anyway Steve obviously has his reasons, who am I to question that, either way it's certified, but I agree with you , WHY.
 
Why? you would be altering or adding to an existing circuit, making work for yourself there Steve, sorry but I disagree with your logic on the Radial to Ring scenario.
Hi Pete, obviously it goes without saying that there's no problem at all with disagreeing, I was very clear in saying it's what I would do, not what others should do! :)

My reasoning for not using a MEIWC for converting a radial to an RFC is that the current minor works form does not include space for the details for the proper testing of RFCs... although... I suppose you could say that if you're adding another socket to an RFC (extending the ring, not adding a spur) you would need to confirm r1, r2 and rn as well; and I guess you could always write it elsewhere on the form. Just generally looking at what the stated purpose of a MEIWC is, and the examples given, make me think that the two examples stated - changing the OCPD for one of a different type or rating, or converting a radial to a ring - fall outside the intended scope. It's not something I feel strongly about what other people do at all. If someone said, "I'd happily use a MEIWC for converting a radial to a ring," I'd say, "Fair enough, up to you." :)

I note the new MEIWC in the 18th Edition draft for public consultation includes extra bits you need to put in, including r1, r2 and rn. The changes have not been popular with those commenting!

I agree with the principle of not making extra work for yourself. Perhaps as I gain more experience my views will change on this matter. :)
 
My reasoning for not using a MEIWC for converting a radial to an RFC is that the current minor works form does not include space for the details for the proper testing of RFCs

There isn't anywhere on the MEIWC to record any continuity of CPC readings, there is only a tick box to confirm that the test has been carried out with a satisfactory result.
Just because there isn't a designated space to write the results it doesn't mean you can't carry out the test!

There is a big blank space where you could record such information if you so,wished however.

image.jpg
 
There isn't anywhere on the MEIWC to record any continuity of CPC readings, there is only a tick box to confirm that the test has been carried out with a satisfactory result.
Just because there isn't a designated space to write the results it doesn't mean you can't carry out the test!

There is a big blank space where you could record such information if you so,wished however.

View attachment 37613
Perhaps he uses the niceic model forms which have a R1+R2 box to record your results and also a R2 box
 

Reply to Garage Sockets Regulations in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
334
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
540
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top