i may be going mad but cant find in the regs what are the requirements for external sockets, can they be spured of the ring if an RCD is fitted or do they need there own circuit ?
 
i may be going mad but cant find in the regs what are the requirements for external sockets, can they be spured of the ring if an RCD is fitted or do they need there own circuit ?


Either method is fine. If you do spur off the ring make sure it's only one unless you fit an FCU first and also provide 30mA RCD proection if none fitted.
 
Reg 433.1.5 & appx 15 detail ring circuiy arrangements although there is nothing specific for supplying exterior sockets.
 
Hi H.
There is no regulation stating exterior sockets require a dedicated wiring circuit.
On the question of RCD protection , there is a general requirement to provide 30ma protection to All domestic socket outlets [ up to 20a] inside and outside [with certain restricted exceptions ], there is also the 50mm depth reg regarding buried cables in walls etc.

if you need the Reg Nos...411.3.3 & 522.6.7.

Sparkylad.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Garden Sockets
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Hundleton1,
Last reply from
sparkylad,
Replies
4
Views
2,011

Advert