@Megawatt this is not a US-spec generator, it's European spec, so it has only two wires - a neutral and a 240V hot - plus a frame ground. (We don't have 4-wire circuits or twistlocks!) The problem is that the OP has US-spec electrical wiring with a mixture of 120 and 240V appliances and panels with two 120V hots and a neutral. To run the 120V appliances and lights from the generator requires a transformer, or if the generator output winding has a hidden centre-tap, modifying its outlet box to bring that out as the neutral instead and make the existing 240V neutral into a second 120V hot.

As yet we haven't seen inside the generator we don't know whether the tap in the winding exists (it does in some units so they can be sold globally by fitting the correct outlet box). In any case it sounds like the cable to the generator location does not have the 3rd wire to allow for that modification and is difficult to replace. So the best solution so far is to send the generator's 2-wire 240V to the house with neither wire grounded (I.e. make the neutral a hot by not bonding it) and there use a transformer to create a neutral point halfway between the two, and bond that instead. A 3-pole GFCI on the transformer with the bonding connection to the transformer side of the GFCI will provide shock protection both at the generator and in the house and allow the generator frame ground to be connected to a ground rod separately.

A better (although much more expensive) solution is to use an isolating transformer of the full generator power rating to create a completely separate 120-0-120V supply from the 0-240, in which case the neutral and ground of both primary and secondary can be independently bonded and there is no risk of the transformer being overloaded by a heavy load imbalance or 'letting go' of the neutral.
From your explanation here and my test results here, I thought we already established that I have a floating 230V output from the generator's output and not an L (230V) to N (bonded to G) connection? You also mentioned that with an L-N two wire generator, you cannot use an auto-transformer. So there's a high possibility that my generator has that hidden centre-tap inside. I will try and inspect its internals in the following days. If it does, I have no choice but to connect that neutral point to B1's main panel somehow. As for the frame ground of the generator, can I connect it to either the bus bar of the B1 main panel or B2 main panel? Or does it strictly be connected to any ground bar?

@Lucien my mistake I guess I thought he was from the US and I agree with you now that I know what we’re talking about. ?
Lucien pretty much summarized everything in this thread. And btw, my generator is 8KW.
 
I thought we already established that I have a floating 230V output from the generator's output and not an L (230V) to N (bonded to G) connection?

Yes indeed. I was talking in general terms to set the scene for Megawatt. At this size and smaller the generator itself is usually supplied with the winding floating, but in a permanent installation it would conventionally be grounded and then the blue wire would legitimately be called a neutral. It tends to get called neutral anyway just for being blue, even when it's not grounded.
 
@Simon
Six screws andvthe pabel with the voltmeter & sockets should come off. Lets see what's behind it - in particular how many wires come out of the generator itself.

Here you go with the pictures from the gen panel:

20201225_151814.jpg
20201225_151823.jpg
20201225_151845.jpg

20201225_151949.jpg

20201225_151959.jpg


20201225_152011.jpg

20201225_152023.jpg

20201225_152026.jpg

20201225_152033.jpg

20201225_152037.jpg

20201225_152044.jpg

20201225_152100.jpg

20201225_152108.jpg



I'm not sure if those pictures are enough but if not let me know what else I need to check to see if there's a hidden centre-tap somewhere.
 
Also, it does look like I may have found a way to route a 3rd cable from the generator the main panel in B1. It won't look the best but I have no choice at this point but to correct the whole system. As for using an auto transformer versus maybe using the hidden neutral (if it is available), I am waiting for your recommendation.

As for my earthing questions, these are still my pending questions:

1. Is it ok to leave the B1 and B2 ground rods not bonded together?
2. Is it ok to bond the generator (which is just for B1) to the B2 ground rods as it is literally just beside them? I don't see why not because ground rods are only mainly used for lightning strikes anyway and are not for L-E faults.
 
OK, the first thing there is that there isn't a centre tap on the generator - at least, if there is then it's not been brought out into the panel. So you are now down to using a transformer or finding a way to safely run only 220V loads.
You don't need to expose the earth rods to link them. If you can run a cable between the DBs then you just need to bond the two earth bars together. After doing that, there's no reason really not to connect the genny frame to B2's earth bar. It may be worth consulting someone locally to see what your local regs/codes say about sizes of cable to use for these earth connections.

Your earth rods are used for much more than lightning protection. They are an integral part of protection against shock - in the event of a fault, current flows through the earth and causes the supply to disconnect instead of things becoming dangerously live.
 
OK, the first thing there is that there isn't a centre tap on the generator - at least, if there is then it's not been brought out into the panel. So you are now down to using a transformer or finding a way to safely run only 220V loads.
You don't need to expose the earth rods to link them. If you can run a cable between the DBs then you just need to bond the two earth bars together. After doing that, there's no reason really not to connect the genny frame to B2's earth bar. It may be worth consulting someone locally to see what your local regs/codes say about sizes of cable to use for these earth connections.

Your earth rods are used for much more than lightning protection. They are an integral part of protection against shock - in the event of a fault, current flows through the earth and causes the supply to disconnect instead of things becoming dangerously live.
Ok. So what auto transformer capacity am I looking for to be on the safe side? Am I targeting 50% (5.4kVA)? I saw a couple of companies making auto transformers locally so I might as well consult them about this too. And if I understand correctly, would the connections from the gen be like so (after bonding together the DB ground bus bars)?

L1/L2 = direct from gen to B1 DB
G = gen frame to B2 DB ground bus bar
Autotransformer = connected to L1/L2/G output terminal of gen
N = connected from autotransformer output to B1 DB

As for the earth rods, that's what I thought at first. But after reading and understanding about earthing systems from earlier this year, when there is an L-E fault, the current flows through the socket E terminal, yes, and then back to the main panel, and then to the neutral (since it's bonded to ground in the main panel) and then back to the source. This path is very low resistance, so current is high enough to trip the break to disconnect the circuit. Here are some references that explain the same:


So for L-E fault, the N-G bonding at the main panel is what's protecting us. For lightning strikes, it's the ground rods. And for people accidentally touching live wire/caused by wet surfaces, it's the RCD's (whether at the breaker level or at the outlet level) are what's protecting us.

Am I missing something when you said the ground rods are protecting us in the event of a fault?
 
Ok. So what auto transformer capacity am I looking for to be on the safe side? Am I targeting 50% (5.4kVA)? I saw a couple of companies making auto transformers locally so I might as well consult them about this too.
Realistically you should not see more than 50% imbalance unless you have one very high power 120V load, so something in the 5kVA region is fine.

BUT be aware that a lot of low cost autotransformer makes lie about the rating, they will advertise 3kVA but in the small print admit it is only 1kVA continuous, etc. Professional site transformers are a bit more conservative, for example 5kVA intermittent and 2.5kVA continuous.

A telling point is often the weight, a full rating 5kVA transformer is going to weight of the order of 40kg I guess.




So for L-E fault, the N-G bonding at the main panel is what's protecting us. For lightning strikes, it's the ground rods. And for people accidentally touching live wire/caused by wet surfaces, it's the RCD's (whether at the breaker level or at the outlet level) are what's protecting us.

Am I missing something when you said the ground rods are protecting us in the event of a fault?
The rods are part of the ultimate means of connecting to the Earth.

Most countries now have some variation of TN-C-S distribution where the power company uses line and a combined neutral & earth conductor (TN-C) which is then separated at the installation (TN-S) in to the "live" neutral conductor that carries current, and the safety earth that is intended only to divert fault currents until the supply protection kicks in.

However any fault on the combined neutral & earth is very dangerous as any earthed metalwork becomes live via power unable to return via the neutral. Furthermore RCD (GFCI) don't normally isolate on this. In the UK the risk of this for electric vehicle charging as the car could become energised and even a fairly low voltage is a danger when someone is washing a care and rather wet leading to various regulations and equipment designed to try an isolate the earth on a fault.

The approach that the suppliers have to help mitigate this risk it to have multiple earthing arrangements on the supply N&E. In the UK that is (so far) only done by the supplier, but in many other countries (USA, Australia, Ireland, etc) there is a requirement on all installations to have additional earth rods.

Now it is a point of contention that mostly these rods are ineffective to a local fault, but the advantage really comes from having a lot of them so a fault on a feed to, say, 30 properties has both 30 sets of earth rods AND the rough balance of 3-phase to bring the neutral potential down during a fault.
 
Realistically you should not see more than 50% imbalance unless you have one very high power 120V load, so something in the 5kVA region is fine.

BUT be aware that a lot of low cost autotransformer makes lie about the rating, they will advertise 3kVA but in the small print admit it is only 1kVA continuous, etc. Professional site transformers are a bit more conservative, for example 5kVA intermittent and 2.5kVA continuous.

A telling point is often the weight, a full rating 5kVA transformer is going to weight of the order of 40kg I guess.
Ok, I'll take note of this. I have already inquired from some companies and they'll probably get back to me by next week.

The rods are part of the ultimate means of connecting to the Earth.

Most countries now have some variation of TN-C-S distribution where the power company uses line and a combined neutral & earth conductor (TN-C) which is then separated at the installation (TN-S) in to the "live" neutral conductor that carries current, and the safety earth that is intended only to divert fault currents until the supply protection kicks in.

However any fault on the combined neutral & earth is very dangerous as any earthed metalwork becomes live via power unable to return via the neutral. Furthermore RCD (GFCI) don't normally isolate on this. In the UK the risk of this for electric vehicle charging as the car could become energised and even a fairly low voltage is a danger when someone is washing a care and rather wet leading to various regulations and equipment designed to try an isolate the earth on a fault.

The approach that the suppliers have to help mitigate this risk it to have multiple earthing arrangements on the supply N&E. In the UK that is (so far) only done by the supplier, but in many other countries (USA, Australia, Ireland, etc) there is a requirement on all installations to have additional earth rods.

Now it is a point of contention that mostly these rods are ineffective to a local fault, but the advantage really comes from having a lot of them so a fault on a feed to, say, 30 properties has both 30 sets of earth rods AND the rough balance of 3-phase to bring the neutral potential down during a fault.
Does this apply to a TT earthing system (which I have) as well?

I was reading about the TT system here and it specifically mentioned that "there is another ground rod independently installed at the generator/transformer and that there is no 'earth wire' between that and the local ground rod on the consumer side. In the diagram you posted earlier, we are connecting the generator frame ground to the local earthing system. What is the difference?

Also, I was also analysing what @Simon47 said:

You don't need to expose the earth rods to link them. If you can run a cable between the DBs then you just need to bond the two earth bars together. After doing that, there's no reason really not to connect the genny frame to B2's earth bar.
As you know the L1/L2/N input for both B1 and B2 main panels are from the same electric meter (not 100% sure where the tap is but all inputs are 100% from the same meter). Since the neutral and ground bus bars in these main panels are bonded/shorted anyway, the two earth bars are already shorted at the electric meter point. So do I still need to bond the two earth bars explicitly?
 
OK, this is a quick sketch of how I think you'd need to wire things up.
1609006604122.png

it should be fairly self explanatory. You need a 3 pole changeover (c/o) switch between your meter and the DB to switch between the L1,N,L2 of the mains and the L1,N,L2 from your generator & transformer combination. To give some change of making breakers trip in the event of a fault, you need to earth your neutral point - without it, a (say) L1 to E fault will simply make L1 "earthy", N at 110V, and L2 at 220V relative to earth. This means that various things a user might expect to be "earthy" (such as the outer screw contact of a screw in bulb and it's holder) will be live.
Consider also fitting an RCD (GFCI ?) between the transformer and the c/o switch (it needs to be on the c/o switch side of wherever you connect the earth to the neutral).

Where does your supplier earth get split from the incoming supply ? In the UK it is in (or close to) the supplier's fuse holder (a.k.a. service head) as shown by the dotted line.
And do the earths to the two DBs have cores separate to the neutrals, connected to a common earth terminal near the meter ?
What I'm getting at is, do you have earth cables/cores from one DB, to a common earth block near the meter, and then to the other DB - and which are at all times separate from any neutral cables/cores (i.e., if you imagine you removed every neutral conductor in the system, would the earths still be connected) ? If you do then you already have the two DBs bonded together. If at any point the cable/core is shared with the neutral then for safety I'd suggest a separate bonding connection - otherwise you run the risk already mentioned with faults in the neutral of a shared neutral & earth conductor, which can make all the metalwork in an installation be live.


To recap on some earlier bits no I;ve had time to sit down and doodle ...

Without the transformer, this is effectively what you have
1609006604574.png

See how the loads on the two sides of the board are now in series, with nothing but the relative size of the loads to determine how the 220V is split. I think you got this, but as they say, a picture paints a thousand words.

A bit more on what I said about switched neutrals when you were asking about not having any 110V loads connected. You'd need to use a 4 pole c/o switch and separate neutral bars like this
1609006760960.png

Notice that when running on the generator, there is now no neutral to any of the 110V loads. BUT, the c/o switch is effectively turning everything off by cutting the neutrals. This means that all the neutral wiring, wiring that should be made "dead" by switching off, both pins of sockets, the outer screw body of lamps and holders, etc is live - when users might be assuming that they are dead. It should be fairly obvious now why such an arrangement is explicitly prohibited by UK wiring standards, and even if it's not prohibited by yours, I would strongly advise against such an arrangement.


As to transformer rating.

The very worst case is zero load on one side of the board, and a high load on the other. In this case, both halves of the transformer winding are carrying half the load current. E.g., if you had (say) a 10A load on L2, then the transformer would pass 5A through the upper winding from L1 to N, and by transformer action, another 5A would pass in the opposite direction from L2 to N - thus producing 10A out from the neutral connection. The generator would just see 5A load across 220V (= 1100VA). The transformer is handling 5A x 110V x 2 = 110VA; that's 5A in each winding, 110V across each, and 2 windings.

If you (say) added 5A of load from L1 to N, then that would supply half of the 10A needed for the N-L2 loads. Thus the transformer would now supply 2.5A from L1 to N, by transformer action push 2.5A from L2 to N, and thus supply the 5A from the neutral terminal to balance the difference in load currents. The generator would see 7.5A of load at 220V (=1650VA). Note that the transformer is now only handling 2.5A x 110V x 2 = 550VA even though your are running 50% more load.
I had to "refresh my memory" on transformers to get my head round the details for that ?

If you have any difficulty getting a 220V centre tapped autotransformer, then a 110V-110V standard isolating transformer would do equally well - connect N of one winding to L of the other winding and you have a 220V centre tapped auto-transformer.

In theory you could apply all your load to one half of the board = and thus need a transformer rated for the full generator output (8kVA). In practice, that's unlikely as your 110V loads will be split across the sides. Also, your 220V loads will not use the transformer at all.
I'm not sure how auto-transformers are rated - I assume it's for the total load it is running (e.g. 1100VA in the first example above. An isolating transformer is rated on what it can transform, but when connected as an auto-transformer like this, each winding is only carrying half the load - so you'd only need one rated for half the load, i.e. only 550VA for the first example.

So possibly some thought needed as to what is a realistic rating you need - it won't be 8kVA to match the genny.


lastly, I've hinted at this previously. I have no idea what your wiring regs/codes over there have in them, nor what requirements there are for qualifications to carry out this sort of work, nor whether you might have to notify someone of the work. You would be strongly advices to consult someone local who does know what's what in terms of both safe practices and your local laws/regs.
I.e., treat the advice you've been given as what it is - advice from "some bloke on an internet forum".

Simon
 
OK, this is a quick sketch of how I think you'd need to wire things up.
View attachment 63227
it should be fairly self explanatory. You need a 3 pole changeover (c/o) switch between your meter and the DB to switch between the L1,N,L2 of the mains and the L1,N,L2 from your generator & transformer combination. To give some change of making breakers trip in the event of a fault, you need to earth your neutral point - without it, a (say) L1 to E fault will simply make L1 "earthy", N at 110V, and L2 at 220V relative to earth. This means that various things a user might expect to be "earthy" (such as the outer screw contact of a screw in bulb and it's holder) will be live.
Consider also fitting an RCD (GFCI ?) between the transformer and the c/o switch (it needs to be on the c/o switch side of wherever you connect the earth to the neutral).

Where does your supplier earth get split from the incoming supply ? In the UK it is in (or close to) the supplier's fuse holder (a.k.a. service head) as shown by the dotted line.
And do the earths to the two DBs have cores separate to the neutrals, connected to a common earth terminal near the meter ?
What I'm getting at is, do you have earth cables/cores from one DB, to a common earth block near the meter, and then to the other DB - and which are at all times separate from any neutral cables/cores (i.e., if you imagine you removed every neutral conductor in the system, would the earths still be connected) ? If you do then you already have the two DBs bonded together. If at any point the cable/core is shared with the neutral then for safety I'd suggest a separate bonding connection - otherwise you run the risk already mentioned with faults in the neutral of a shared neutral & earth conductor, which can make all the metalwork in an installation be live.


To recap on some earlier bits no I;ve had time to sit down and doodle ...

Without the transformer, this is effectively what you have
View attachment 63228
See how the loads on the two sides of the board are now in series, with nothing but the relative size of the loads to determine how the 220V is split. I think you got this, but as they say, a picture paints a thousand words.

A bit more on what I said about switched neutrals when you were asking about not having any 110V loads connected. You'd need to use a 4 pole c/o switch and separate neutral bars like this
View attachment 63229
Notice that when running on the generator, there is now no neutral to any of the 110V loads. BUT, the c/o switch is effectively turning everything off by cutting the neutrals. This means that all the neutral wiring, wiring that should be made "dead" by switching off, both pins of sockets, the outer screw body of lamps and holders, etc is live - when users might be assuming that they are dead. It should be fairly obvious now why such an arrangement is explicitly prohibited by UK wiring standards, and even if it's not prohibited by yours, I would strongly advise against such an arrangement.


As to transformer rating.

The very worst case is zero load on one side of the board, and a high load on the other. In this case, both halves of the transformer winding are carrying half the load current. E.g., if you had (say) a 10A load on L2, then the transformer would pass 5A through the upper winding from L1 to N, and by transformer action, another 5A would pass in the opposite direction from L2 to N - thus producing 10A out from the neutral connection. The generator would just see 5A load across 220V (= 1100VA). The transformer is handling 5A x 110V x 2 = 110VA; that's 5A in each winding, 110V across each, and 2 windings.

If you (say) added 5A of load from L1 to N, then that would supply half of the 10A needed for the N-L2 loads. Thus the transformer would now supply 2.5A from L1 to N, by transformer action push 2.5A from L2 to N, and thus supply the 5A from the neutral terminal to balance the difference in load currents. The generator would see 7.5A of load at 220V (=1650VA). Note that the transformer is now only handling 2.5A x 110V x 2 = 550VA even though your are running 50% more load.
I had to "refresh my memory" on transformers to get my head round the details for that ?

If you have any difficulty getting a 220V centre tapped autotransformer, then a 110V-110V standard isolating transformer would do equally well - connect N of one winding to L of the other winding and you have a 220V centre tapped auto-transformer.

In theory you could apply all your load to one half of the board = and thus need a transformer rated for the full generator output (8kVA). In practice, that's unlikely as your 110V loads will be split across the sides. Also, your 220V loads will not use the transformer at all.
I'm not sure how auto-transformers are rated - I assume it's for the total load it is running (e.g. 1100VA in the first example above. An isolating transformer is rated on what it can transform, but when connected as an auto-transformer like this, each winding is only carrying half the load - so you'd only need one rated for half the load, i.e. only 550VA for the first example.

So possibly some thought needed as to what is a realistic rating you need - it won't be 8kVA to match the genny.


lastly, I've hinted at this previously. I have no idea what your wiring regs/codes over there have in them, nor what requirements there are for qualifications to carry out this sort of work, nor whether you might have to notify someone of the work. You would be strongly advices to consult someone local who does know what's what in terms of both safe practices and your local laws/regs.
I.e., treat the advice you've been given as what it is - advice from "some bloke on an internet forum".

Simon
The schematics you've posted depict what I have in mind (based on all the discussions in this thread) so it's good that I'm on the same page as you guys. The only differenxe is that the N and E are bonded together in the main panel of both DB's. So in your schematic, the bonding happens in the house side of the c/o switch, not in the meter or gen/transformer side. @pc1966 pretty much drew what I mean in his previous post:


As to where the supplier splits the earth from the incoming supply, I don't know and I'm not sure if there's an easy way to know just by looking our meter. Also, as I understand it a TT system doesn't warrant that the supplier ground rod be bonded to the local/house grond rods, right? Yes, the separate ground rods of B1 DB and B2 DB have separate cables/cores from that of the neutral cores/cables but do not go back to the supplier ground rod. But yeah, what you're saying about bonding both DB ground rod sets (2 of each, so a total of 4) does make sense now when you said that their "link" should not rely on a shared neutral in case of any neutral faults.

I'd have to search a bit more of autotransformer availability here but I think it's the cheapest option for me now. An isolating transformer would cost much more expensive IIRC.

As for the earlier bits, yes I understand what you're trying to say about all loads being series to each other without the neutral from the generator and how a switched neutral is bad.

There are standards in our country but the problem is that they aren't strictly implemented unless it's for a commercial building or of the similar type. But I get what you're saying. I think the least I need to make sure of are the cable gauges I need to use when adding to the system.
 

Reply to Generator feed to 2L+1N system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
420
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
567
Good day all, I'm writing from the Commonwealth of Dominica (NOT Dominican Republic) where we have single phase 230V, 50Hz. I'm managing a...
Replies
3
Views
1K
How should grounding be made to a 20kVA single phase generator set feeding a domestic property via a manual change over switch? At the generator's...
Replies
17
Views
3K
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
318

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock