Hi all,

I've just completed a 3-phase installation for a Wurlitzer Cinema organ that is being installed into the Troxy (previously a cinema, now a multi purpose venue) in East London.

The next stage of the installation is the design (and eventually installation) of the connection of the large motors which form the massive air blowers that provide the air to power the organ pipes.

We have a limited power supply available (the motor supplies are currently breakered at C40), and the motor specs are as follows:

  • 380-440V AC 3-Phase
  • 15HP
  • 21A Continuous Current

We have 2 of these to install (one for each side of the cinema), and so I need to find a pair of soft starters suitable for handling the starting load, within the limits of the C40 breakers.

Can anybody advise on a suitable unit to carry out this job? I can cope with most things, but i'm not quite as knowledgeable on motors as I would like to be, so I thought it best to ask advice from fellow electricians than spec the wrong product for the job!

Many thanks in advance,

Rob :)
 
Contact Telemecanique, the reason I say this is:
A/ they are helpful
B/ they are reasonably easy to set up
C/ replacements are readily available (not that you should need them)

One thing to add, put an interlock between the two starters so that fan “A” is up to speed before fan “B” starts. The soft starts will ease the starting load, the delay will ease the total load.
 
You'll need an 11 kW soft starter for each motor. 11kW is available in some of the compact ranges depending which manufacturer you prefer. You can try Danfoss which are fairly solid kit.

As far as running current goes, the 21Amps, which I assume you got off the motor info plate, is most likely FLA specs. The actual run current will be determined by the load the motor is under so it should be somewhat less than that.

It might even be worth trying the motors without a soft start, you could possible swap the MCB for a D curve and stagger the starts of the motors with a short time delay (a few seconds) on one of them.

Edit; Excuse any repeat info, got beaten to the post by Tony :)
 
Contact Telemecanique, the reason I say this is:
A/ they are helpful
B/ they are reasonably easy to set up
C/ replacements are readily available (not that you should need them)

One thing to add, put an interlock between the two starters so that fan “A” is up to speed before fan “B” starts. The soft starts will ease the starting load, the delay will ease the total load.

I have had many dealings with telemechanique and i must agree their products are not only of high quality/ease of use but the customer support and queries are very good!
Also /agree with the interlock, we use the same method on our *chopfans* at my place of work since they are each ~11kw they are sequencially started to avoid that nasty inrush of all coming on at once :) .
 

Reply to Help Needed in selecting a Motor Soft Start in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm sorry if this isn't in the right place but this is my first time using this forum. I'm also sorry if i make some mistakes but I'm new to this...
Replies
6
Views
1K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hi, I'm looking for some guidance from more experienced hands. Have a friend who just bought a 2.2kw air compressor which is obviously blowing...
Replies
20
Views
4K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock