If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
 
Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
That would be 4mm wouldn't it?
 
I would more than likely add them together and make a note on the cert reflecting the amount of cables on the circuit.
 
That would be 4mm wouldn't it?
I think Pete is correct there being a minimum of 4mm single earth when protected against mechanical damage.
If you are saying you have a 2.5/1.5 radial with a 2.5mm earth from the end of the radial to the distribution board I would put down 1.5 as the circuit CPC. What is the installation method?
 
Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
Because that’s just one conductor.
 
That would be 4mm wouldn't it?
I think he is referring to the 1.5/1.5 of a ring final circuit. It depends on the schedule format you are using and whether you can insert all conductor csa. I like to include all as I hand write them so if you have a 2.5 T&E with a separate 4mm cpc I would put 1.5/4.0
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Zdb

~
Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
High integrity earthing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Zdb,
Last reply from
westward10,
Replies
5
Views
1,965

Advert