Paddy-08

New EF Member
Hi. I’m new to this but was woundering if anyone has had this problem. My immersion heater keep tripping the mcb when the timer switches it off. The mcb won’t reset unless the timer is set to on which works fine but as soon as the timer is up it trips the mcb again. The timer I have is a Horstmann Economy 7 quartz. Thanks for ur help
 

Wilko

Electrician's Arms
Hi Paddy and Welcome to the Forum.
Sorry to hear you've got an electrical problem, but hopefully someone will be able to help :)
Can you have a close look at the switch that trips and report back what it is? e.g. it may have B16 written on it? Or is it the RCD (one with a test button) that trips?
 

Paddy-08

New EF Member
Hi how are you? And I hope so it’s doing my head in it’s the main RCD with the test button on. It’s worked fine and then just tripped in the night
 

Lagentium

Regular EF Member
Paddy are you an electrician? If so I'd connect it straight through and take the timer out of the equation and turn it on and off via the local spur and see if it trips. If you aren't qualified then get someone who is to have a look and they may do the same mate.
 

Paddy-08

New EF Member
Yes that would make sense and I think it’s must be the timer. But if the timer is set to off I can’t reset the RCD
 

buzzlightyear

please let me back in to the prison cell.
Electrician's Arms
get a plumber in and ask him to test it for you .the reason the element if it needs changing by a plumber .not a sparky because of the head .
 

Dave OCD

Forum Mentor
Electrician's Arms
Trainee Access
Buzz I don't think your average plumber would have a clue about electrically testing an immersion element.
 

Dave OCD

Forum Mentor
Electrician's Arms
Trainee Access
Yes possibly - and test equipment. I'd say electrician to test, plumber to change element if necessary.
 

shaun1

Regular EF Member
If it is not possible to reset the RCD at all with the timer in the off position, then this sounds like a fault with the timer (or a relay it controls). Perhaps the NC contact is connected earth or similar.
 
Status
Not open for further replies.

Electrician Talk

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.
Top