M
m4tty
Hi,
I was just wondering if anyone out there could explain how to calculate the impedance of a circuit containing combinations of the above. For example
Series Circuit containing 6 Ohms resistance and 8 Ohms Capacitive Reactance. Calculate impedence??
Thanks in advance.
Matt
er cant draw out the formula but will try
Z (total im) = root squared of Rsquared + Xc squared
if inuctance was in circuit it would be deducted from Xc or vice versa
from distant memory... I think that impedance (z) is equal to the square root of (resistance (r) squared plus reactance (x) squared
Treat it as a right angled triangle (Pythagoras)
Impedance (Z) is the hypotenuse.
Resistance is the adjacent.
Reactance is the opposite.......where you have Xc and XL one leads and the other one lags so the resultant (one take away the other) is the value you use as per Mr Pythagoras' theorem.
You can then find youe Power Factor with cos, ADJ/HYP
you will find in most of these questions involving pythagoras that they give you it will be a 3,4, 5 triangle (or multiple of eg 6,8,10 or 30 40 50 etc etc) the hypotenuse being the impedance. If you remember that it will help you to quickly check answers
So in your example above 2 of the sides are 6 and 8 so the hypotenuse/impedance is 10 ohms.
[or the square root 6^2 + 8^2 = 10]
Impedance, Reactance, Resistance
Thread Tags
m4tty,
pushrod,