Hmm. Not just for pipesDoesn’t BS951 specifically state those comps are for pipes?!
“Other means of earthing” could include the armour of the SWA. So maybe it complies with BS951?
NO IT DOES NOT
Note 1 Specifically says that these clamps are not intended for the connection to the armour or sheath of a cable. !!!
probably contravenes 512-05-01 too.