H

Hutch118

Hi Lads,

Need advice on the installation of a CNC Turning Centre. The Full Load of this machine according to the plate rating is 90kva but in reality, when the machine is running, it takes a fraction of this load.

What I need is recommended cable size, fuse/breaker size. Length of cable ruins 45m clipped direct and running beside a few other cables. I've already done my calculations but the cable size seems excessive for the load I know is going to be taken off the supply.

Can anyone help me out on this please?

Thanks. Hutch
 
What size cable have you calculated?

The manufacturers have stated 90KW, do you know something the manufacturers don't.
 
Last edited by a moderator:
What size cable have you calculated?

The manufacturers have stated 90KW, do you know something the manufacturers don't.

Hi Tony, the manufacturers plate states 90 kva which is 72kw, I know from past experience on very similar machines that in reality, they will run at a fraction of the stated power requirements, I suppose it's diversity within the machine?
Cable calculated is 35mm 4c but wondered if I could go down to 25mm. I suppose I answer my own question when I realise the cable has to be able to carry the FLC stated on the machine. (Eg, a machine rated at 60kva takes 30 amps when running in the workshop just now.)

Hutch
 
Power formula watts = V I COS Phi
Where cos Phi is power factor so 72 kw seems right then split over three phases about 25 kw per phase divide by 230 gives just over a hundred amps .not checked the regs for vd and current capacity but its a fair length run so i would go with the 35 mm . The 25 mm would as you say probabaly do so its useful to look at a similar machine and measure its current doing work and feel the temperature of the cable while doing work. On and off time ratio has a big effect on the cooling of the cable also as does the ambient room temp so common sence could come into play if you find a similar machine in the same shop takes 70 amps for a couple of minutes then stops for 2 minutes whilst the operator does another operation then maybe the 25 mm but if its basically running continuously at full load then i would opt for the 35 mm but i'd do the calcs for vd and correction factors to be sure
 
The 90KVA will take in to account for working the heaviest job the machine can handle and diversity shouldn't be applied here as you cant be sure the use of the machine or the work done won't change, the very nature of the CNC machine means its versatile and adaptable to new work loads and programmes, you never can predict the demand put on this machine as new customers and orders may come in at any time.

Ive just fitted 5 CNC supplies of varying sizes and would never dream of applying diversity to a machine of this nature unless exceptional circumstances meant i could.
 
Last edited:
Can you tell us the front end fusing device as this too will have a bearing on the cable size ...
e.g. If your using HRC fuses you are fixed to choosing the available fuse ratings and this could add additional CCC to your cable to ensure your fuse rating is less than the CCC of your cable.
 
The 90KVA will take in to account for working the heaviest job the machine can handle and diversity shouldn't be applied here as you cant be sure the use of the machine or the work done won't change, the very nature of the CNC machine means its versatile and adaptable to new work loads and programmes, you never can predict the demand put on this machine as new customers and orders may come in at any time.

Ive just fitted 5 CNC supplies of varying sizes and would never dream of applying diversity to a machine of this nature unless exceptional circumstances meant i could.

Probably not what I meant Darkwood in respect to 'diversity', wrong use of the term. The machine is rated 90 kva, when this runs, the load measured even during heavy cuts is relatively low. I obviously realise that the cable I need to use to supply it has to take the FLC.
 
Can you tell us the front end fusing device as this too will have a bearing on the cable size ...
e.g. If your using HRC fuses you are fixed to choosing the available fuse ratings and this could add additional CCC to your cable to ensure your fuse rating is less than the CCC of your cable.

Will be supplied from a fused switch at 200A rating thru 125A HRC fuses, motor rated.
 
As i calculate it 90KVA 3phase is 130amps im unsure where you work out 125amps is big enough as front end devices your front end fuses may have to be 160amps depending on switch/fuses typical fuse ratings hence i brought this up when i spotted 35mm cable been considered.
 
As i calculate it 90KVA 3phase is 130amps im unsure where you work out 125amps is big enough as front end devices your front end fuses may have to be 160amps depending on switch/fuses typical fuse ratings hence i brought this up when i spotted 35mm cable been considered.

Its 160A on the front end and 125A at the switch inside the machine. Apologies.
 
Well you need to leave as is for discrimination in event of overload but although i dont entertain running parallel supplies on anything less than 95mm you could do so as this will reduce cable costs at the present (without working out ) i suspect your looking at a 70mm 4c but running 2x 25mm 4c with satisfy the front end fuse rating and reduce copper csa needed.
Im a little confused as you already preposed 35mm but then you say the front end switch fuse protecting the cable will have 160amps fuses it dosnt make sense????
 
Last edited:
Try not to change your story too much it makes you look unproffesional (not an accusation), you originally asked about reducing 35mm to 25mm and this raised my front end fuse question to which you said 160amps... well i think you know where im coming from as your CCC rating of the cable must be larger than the device protecting it (excluding exceptions for this conversation).
 

Reply to Installation of a 90kva CNC Machine in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi all, I have been asked to install individual three-phase supplies for a band saw and table saw. Having trouble figuring out the correct cable...
Replies
15
Views
2K
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
Replies
10
Views
4K
Hi, I'm a self-build amateur - I'll be running cables and getting system sign-off/inspection by certified competent person, and am just working...
Replies
6
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock