I have earthed the metallic sheath of SWA cable by wrapping around the bare earth wire (sleeved off) around a bolt and tightened on to the brass eyelet using a nut as shown in the picture.

IMG_0062.jpg

Is this acceptable? or should I really crimp it using the one shown on the picture below and bolt it on to the brass eyelet?

Eyelets.jpg

Any feedback will be much appreciated.
 
Crimp it, the copper will squash over time and become loose, I also double nut it to make sure it stays tight.

And it looks crap! :D
 
  • Like
Reactions: 4 people
Crimp it every time IMO have never be a big fan of copper wrapped around bolts.

Whats with the big nick in the cable bedding? hope it aint gone through any of the insulation!
 
Last edited:
  • Like
Reactions: 4 people
Echo the above comments re the sheathing.

I would normally put the bolt through the base of the enclosure as well, more secure that way.
 
  • Like
Reactions: 1 person
As above always crimp. Also I always use brass bolt!

Can't say I'd use a gutter bolt either - Whats wrong with a proper brass pan screw? Also I agree with Truckster about using double nuts. Sorry mate but even for purely cosmetic reasons I would be happy with that.
 
Last edited by a moderator:
To be fair to the OP, the current syllabus of the 2330 states that "roofing bolts" should be used and not drilled through the case as to maintain the ip rating, tripe I know as I use brass panel screws and bolt thro but that is what is being taught at the moment
 
  • Like
Reactions: 1 person
to be fair to the op, the current syllabus of the 2330 states that "roofing bolts" should be used and not drilled through the case as to maintain the ip rating, tripe i know as i use brass panel screws and bolt thro but that is what is being taught at the moment

wtf!!!
 
  • Like
Reactions: 1 person
To be fair to the OP, the current syllabus of the 2330 states that "roofing bolts" should be used and not drilled through the case as to maintain the ip rating, tripe I know as I use brass panel screws and bolt thro but that is what is being taught at the moment

Fair enough if it has a suitable IP rating to maintain, that makes sense. That's one of todays lessons :D
 
another argument based on the supposition that rain falls up, not down. any IP rated box i fit, i drill a drain hole in the bottom. seen so many so called IP65 boxes half full of water.
 
  • Like
Reactions: 3 people
Im with tel on this one i always drill a drain hole at the bottom of IP rated items , MK master seal range have drain holes , unless its going under water that is , i have to admit i do use roofing bolts but instead of the horrible square nut i use Nylocks aint going no where then
 
  • Like
Reactions: 2 people
Thanks for all the inputs, seemed like lesson time and I have learnt a few things. As Amp David says, I too love to use brass nuts/bolts but couldn’t find suitable ones and I am hence sticking to what I have used earlier. Really wanted to use “Piranha Earth Locking Nuts” but my local shop or the “Bigshed” doesn’t do them.

I have taken your advice on board and have crimped it with suitable eyelet. The IP rating of the box hasn’t been compromised as the hole I drilled was big enough just to thread the lug-nut thro’.

Cheers!
 
Yeah, they guys are right. Crimp, crimp and crimp. double nut and don't forget your washers and copper grease!

And be a little more careful with whatever you are striping the outer sheath of with. Looks like a stanley blade incident to me.

Just out of interest, did you split the cores on the earth cable? Seen this done countless times and given out many b*llockings for it.
 
  • Like
Reactions: 1 person
Should have used a crimp for sure and i have always used 2 nuts on a banjo in a plastic enclosure. You cannot make a good reliable electrical connection by clamping the banjo onto plastic. Use 2 nuts on the gland with the banjo sandwiched between them.
 
Should have used a crimp for sure and i have always used 2 nuts on a banjo in a plastic enclosure. You cannot make a good reliable electrical connection by clamping the banjo onto plastic. Use 2 nuts on the gland with the banjo sandwiched between them.

Biggest echo ever here. Always 2 nuts on the banjo for me aswell. Thought I was the only one!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
Website
http://www.brithome.com/

Thread Information

Title
Is this acceptable?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
21

Thread Tags

Tags Tags
acceptable

Advert

Thread statistics

Created
Goody,
Last reply from
Dunc,
Replies
21
Views
2,449

Advert