I have a quick question, I have my part p inspection on Friday, I have changed my CU as my competed job for inspection as it needed doing anyway however I have one question.

I fitted a split board, it came with one isolation switch and one RCD, I am on a TT system so I wanted full protection and changed the isolation switch for a second RCD, now I have set if up with the first RCD looking after light up and sockets down and the second RCD with the opposite bit with the shower added to that.

Now as I have done this I don't have a one main isolation switch on the board, to isolate everything you have to turn off both RCD's, is this ok?

I have checked the regs and all it states is circuits must have a method of isolation that it double pole Whitchurch my RCS's are
 
AFAIK you still need a main switch as a single point of isolation for the entire installation. (537.1.4)

Didn't you have enough room in the board to just add the second RCD instead of replacing the Main Switch?

Or better still, why didn't you buy a 17th Ed board? Sounds like you've fitted a 16th.
 
I did the same and fitted an external mains switch next to the cu.
 
sounds like 17th CU meant for use with circuits not requiring rcds and those that do require rcd protection beleive it or not not every instalation requires total rcd protection

as for changing the main sw for an RDC you havent got discrimination so realy defeated the point in fitting 2 RCDS ie Your First RCD is likley to trip at same time as the second one
 
Last edited by a moderator:
sounds like 17th CU meant for use with circuits not requiring rcds and those that do require rcd protection beleive it or not not every instalation requires total rcd protection

as for changing the main sw for an RDC you havent got discrimination so realy defeated the point in fitting 2 RCDS ie Your First RCD is likley to trip at same time as the second one


looks like you rite the board was setup for split load with some not rcd protected, when i added the second rcd i spotted the discrimination problem so i set it up so that both RCD were fed from the meter tails rather than one feed from the other.

the meter tails come into the first RCD then are looped out to the second RCD with the supplied internal cables, the unit has 2 separate neutral bars so it was straight forward to do, however i have this isolation problem as i previously mentioned, iv just had another look and i have room for a switch as well (just) but i will need some more internal cables, i will also have to move the bottom live bar over a bit as well,

if i add the isolation switch then feed both RCD's of that with 4 internal cables (2 l & 2 N) that should be fine ?
 
I would say it'll probably be easier to install an external isolator as the lads have suggested.

Just make sure you point out to your assessor that you have re-configured the CU in order to provide discrimination.
 
why didnt you just fit a board with a main switch and dual rcds you can pic em up for £50 ,i would have fit this and a seperate 100mA isolator before the board, because of your tt system. make sure the ze and zs are acceptable
 
why didnt you just fit a board with a main switch and dual rcds you can pic em up for £50 ,i would have fit this and a seperate 100mA isolator before the board, because of your tt system. make sure the ze and zs are acceptable

No need for 100mA if all circuits are protected by 30mA (as in a 17th Ed Dual RCD)
 
the 100mA main isolator before the board to reach your dissconection time, as i said check your ze- zs values . remember regs are guidance common sense is much more important
 
the 100mA main isolator before the board to reach your dissconection time, as i said check your ze- zs values . remember regs are guidance common sense is much more important

As JUD says, dual 30mA RCDs in a 17th ed. board will achieve this.

I am more impressed that the OP's predictive text thinks 'which' is 'Whitchurch' :D
 
thanks for all the advice, when i got the board i assumed it was a full split load twin RDC board, only once i started installation i realised it was split load bit with only one RCD (damn Wickes) any how today i managed to squeeze in the main switch again and feed the two RDS from that as i had some 80A meter tails left from another job so i used them to cable it, its very tight in there but everything fist snug;)

i have added below pick of the CU finished, please ignore the tape on the lives i have now removed that it was just for identification, any one see any issues that could give me problems with the inspection ?

i appreciate your feedback as its my first board change.

ca11018f.jpg
 
its a mess is the first thing that springs to mind , looks a real d.i.y job, tales are non harmonised , not stripped correcty should not be seeing that red,poor terminations-copper showing, none of the neutrals or cpcs correspond , no cover over busbar,looks like a 40amp supplying 6mm2 , i know it sounds awful,l just read its your 1st change but you really should know better , personally i would take it off and start again, try curling the wires neatley cct1 should match neutral and cpc 1 , make sure you put all relevent labells on it aswell. sorry for being so harsh but i see far too many so called sparks pulling stunts like this
 
Unfortunately I have to agree with the post above. I know it is your first, so please try and take the criticism constructively.For gods sake get a bus bar cover on the install. Neaten it up and make sure all the cores correspond to the correct circuit number, it is so frustrating when it comes to testing an older board and you have to trace every core. Have a little look at 'show your installs' and see how experienced sparks do it. It is not hard, but it takes a bit of practice and guidance.
 
On a positive note you have left the conductors long as they should all reach the furthest corner of the board. I know thats not always possible with a board change as they've already been chopped.
I seen a new build the other day and they were all cut off to just reach terminations thus no room for future changes.
Also you have put them in cpc, neutral and then line so thats correct.

Good on you for putting it up. Taking the constructive criticism to learn.

I too would take it all out and redo for the extra practice
and make sure all terminations are firm as I looked at a messy board once touched one conductor and it fell out.
 
Last edited by a moderator:

Similar threads

D
Replies
5
Views
4K
UK Electrical Forum
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Isolation switch help ? I
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
Hundleton1,
Last reply from
martysparky,
Replies
18
Views
5,593

Advert