Hi,
could someone tell me how to calculate the actual disconnect time from a log table and where I can find this table for a 6A RCBO made by British General. I need this to get a meaningful CPC CSA using the adiabatic equation.

Many thanks,

g
 
Do you have a copy of the 18th edition Regs book or onsite guides?
hi yes i do have both and if you are saying i should use fig 3A4 that's ok but i have a fault current of 301A and if I take 0.4 seconds as t then I end up with a cross sectional area of >1.66mm. can I use the lower trip time of 0.1 seconds?
thanks
 
Adiabatic Equations.PNG
 
thanks telectrix but can you tell me how to justify its use? thanks,
g
Take a look at the fault curves in appendix 3 of BS7671. For type B and C breakers/RCBOs, if it meets any permitted disconnection time, even 5s for distribution circuits, then it disconnects at 0.1 seconds (or faster). There is no middle ground, as above a certain current the magnetic trip will operate and will disconnect instantaneously. For example, you can't make it disconnect in exactly 1 second.

As you are presumably using a B or C type breaker/RCBO, use the fault current at the origin of the circuit for the calculation. For these devices, let through energy tends to increase with fault current, and fault current is greatest at the origin. This is the most onerous point in the circuit.
 
For MCB and RCBO in the thermal part of the trip curve you can use the graphs to get a meaningful measure of I2t for the adiabatic equation.

Once you hit the "instant" magnetic point though those plots are pretty meaningless. For an accurate figure you need to get the manufacturer's plot of let-through energy (i.e. I2t as a function of PFC) and some of the better makes provide this (e.g. Hager in their commercial catalogue). Otherwise you can refer to the generic specifications for that class of energy-liming breaker, for example Table B7 in the On-Site Guide.

Attached is an example page from Hager's catalogue.
 

Attachments

  • letthroughenergyhager.pdf
    98 KB · Views: 4
It applies to all protective conductors,
Technically yes but practically I have never done an adiabatic for circuits issuing from the MCB as the fault current is automatically held to the level of the MCB. However, the main earth from the CU to the Neutral terminal where there is no protection, yes I can see the use of the adiabatic there as if the main earth goes meltdown there is a problem. But for 2.5 cable do you really do an adiabatic? What can you do if 1.5mm² is not enough? Thread a thicker cpc up the cable. Sorry If I am being a bit thick here but ready to learn something new.
 
Technically yes but practically I have never done an adiabatic for circuits issuing from the MCB as the fault current is automatically held to the level of the MCB. However, the main earth from the CU to the Neutral terminal where there is no protection, yes I can see the use of the adiabatic there as if the main earth goes meltdown there is a problem. But for 2.5 cable do you really do an adiabatic? What can you do if 1.5mm² is not enough? Thread a thicker cpc up the cable. Sorry If I am being a bit thick here but ready to learn something new.
You are quite right.

For any of the "standard circuits" you don't need to bother with the adiabatic as the cable size versus OCPD is already fine. That really is why using the usual suspects (standard cases, such as Table 7.1(i) from OSG) makes so much sense as it is one of many less things to worry about design-wise!
 
Last edited:
Technically yes but practically I have never done an adiabatic for circuits issuing from the MCB as the fault current is automatically held to the level of the MCB. However, the main earth from the CU to the Neutral terminal where there is no protection, yes I can see the use of the adiabatic there as if the main earth goes meltdown there is a problem. But for 2.5 cable do you really do an adiabatic? What can you do if 1.5mm² is not enough? Thread a thicker cpc up the cable. Sorry If I am being a bit thick here but ready to learn something new.

You are quite right.

For any of the "standard circuits" you don't need to bother with the adiabatic as the cable size versus OCPD is already fine. That really is why using the usual suspects (standard cases, such as Table 7.1(i) from OSG) makes so much sense as it is one of many less things to worry about design-wise!
Is this correct? The reason I query it is table B7 on p132 of the OSG. It shows minimum CPCs for class 3 B and C type MCBs, for different fault current levels.

For example, a B32 at a fault current of up to 3kA has a minimum CPC of 1.5mm. Above that and up to 6kA, it would be 2.5mm - thicker than the usual 1.5mm CPC that you'd typically find on a ring wired in 2.5mm T+E.

Is there something else at play here?

Calculating CPC size using manufacturer's data usually gives a much smaller min. CPC than those listed in table B7, but not always. BG and Contactum, when asked, gave identical data (which I suspect comes from the product standard rather than their own tests) which, when run through the adiabatic, gives the same results as table B7 for the higher 3-6kA fault.
 
Is this correct? The reason I query it is table B7 on p132 of the OSG. It shows minimum CPCs for class 3 B and C type MCBs, for different fault current levels.

For example, a B32 at a fault current of up to 3kA has a minimum CPC of 1.5mm. Above that and up to 6kA, it would be 2.5mm - thicker than the usual 1.5mm CPC that you'd typically find on a ring wired in 2.5mm T+E.

Is there something else at play here?
I think it is down to the ideal case of DB PFC and max let-through of the MCB standard, and the real-world case of MCB generally being better, and the actual PFC being less.

For example, if you have a DB with 6kA PFC (assuming for now 230V) then your Ze is around 0.038 ohm. To bring that down to 3kA you need to double that, and with the R1+R2 of 2.5mm T&E being around 19.5mOhm/m that is 2m of cable.

So for most faults on any real-world installation using typical circuits you won't reach cable-damaging I2t, and if you do it will only be the first metre or so before a very close (and very hard) fault that needs replacing.
 
I think it is down to the ideal case of DB PFC and max let-through of the MCB standard, and the real-world case of MCB generally being better, and the actual PFC being less.

For example, if you have a DB with 6kA PFC (assuming for now 230V) then your Ze is around 0.038 ohm. To bring that down to 3kA you need to double that, and with the R1+R2 of 2.5mm T&E being around 19.5mOhm/m that is 2m of cable.

So for most faults on any real-world installation using typical circuits you won't reach cable-damaging I2t, and if you do it will only be the first metre or so before a very close (and very hard) fault that needs replacing.
Ah, I see, that puts it in perspective!
 
Take a look at the fault curves in appendix 3 of BS7671. For type B and C breakers/RCBOs, if it meets any permitted disconnection time, even 5s for distribution circuits, then it disconnects at 0.1 seconds (or faster). There is no middle ground, as above a certain current the magnetic trip will operate and will disconnect instantaneously. For example, you can't make it disconnect in exactly 1 second.

As you are presumably using a B or C type breaker/RCBO, use the fault current at the origin of the circuit for the calculation. For these devices, let through energy tends to increase with fault current, and fault current is greatest at the origin. This is the most onerous point in the circuit.
Thanks pretty mouth.
 

Reply to log tables for actual disconnect time in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
803
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
539
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock