An RCD DOESN'T protect against overload or a line/neutral short-circuit.
So on a new split phase 17th edition board with 2 x 30mA RCDs.. If a line/neutral short circuit occurs what trips anything?
As there are now no MCBs?
An RCD DOESN'T protect against overload or a line/neutral short-circuit.
Ignore.
Have I missed something???
*EDIT* Just seen your question in Jurasic Spark's quote.