personally, i always do r1,r2,rN, if only to 1. ensure the |RFC/s have not been split. and 2. to make sure i don't get my tiny mind confused and cross connect the legs in the CU.
 
personally, i always do r1,r2,rN, if only to 1. ensure the |RFC/s have not been split. and 2. to make sure i don't get my tiny mind confused and cross connect the legs in the CU.

I also do this, but for another reason too, because on a couple of jobs I have had an r2 reading lower than one r1 or rN readings, the cause has always been a loose connection in one of the SO's,
a Zs reading would not show a loose N.
 
  • Like
Reactions: 1 person
I've got to admit I don't see why you wouldn't do r1, r2, rn when you change the CU. It is a 30 second job when you have all the wires out and means you can fill in the test schedule fully. Cross coupling and doing R1+R2 is a bit of pain and I can see that a quick check of r1, r2, rn against your Zs tests would do the job there.
 
had one the other week. r1 = 0.45, r2 = 0.70. rN = open circuit. found it in a S/O, terminal loose.
 
lol looks like I've lost this one lads ......................but to all of you fair dos for doing the job to the nth degree
 
had one the other week. r1 = 0.45, r2 = 0.70. rN = open circuit. found it in a S/O, terminal loose.

ditto, but to be fair Malc said he would test L-N as part of his Zs testing which should pick up the neutral fault.

I also had one the other week on a lighting radial where Zs looked ok (ish) along the circuit but a proper R1+R2 (with earth disconnected at the board) found a break in the cpc. For the 2nd half the circuit the cpc came from the other lighting circuit- connected at at a dual gang switch. You could argue that for a board change, who cares, there was still a cpc at each outlet but it is one that I would want to know about.
 
Cross coupling and doing R1+R2 is a bit of pain and I can see that a quick check of r1, r2, rn against your Zs tests would do the job there

I have on the odd occasion had a fine r1,r2 and rN reading at the CU, but an iffy reading at a SO when doing the cross connected tests, and found the SO connection loose, but the wires twisted together in the slack terminal.

I tend to just do the full tests because it is my head on the block so to speak, when the assessor told me the only defence I have is my paperwork, I take it the scheme provider won't be in the dock defending me.
 
Last edited by a moderator:
  • Like
Reactions: 2 people
the only thing scheme providers would defend is their fat fees.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New C U Certification
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
Tucosweep,
Last reply from
telectrix,
Replies
27
Views
2,743

Advert