Patrickquinn

Anyone help me I have 14 235w rec panels on 2 strings 7 per string but the inverter doesn't click on under normal light levels because of the voltage isn't enough per string can I put 8 panels on one string and 6 on the other to bump the voltage up for the inverter
 
I have done loads of pv installations. This is a job done by someone else it has a sunnyboy 3300 Which needs a stable voltage of 250 to start up but at 200 w/m2 the voltage is only about 240 and the inverter stays in grid monitor mode
 
Wrong inverter, end of story, add more panels or swap the inverter. Just Download and run it through SunnyDesign, you'll see for yourself the problem.
 
I have done loads of pv installations. This is a job done by someone else it has a sunnyboy 3300 Which needs a stable voltage of 250 to start up but at 200 w/m2 the voltage is only about 240 and the inverter stays in grid monitor mode

Sorry to sound so harsh but the system hasn't been designed properly and some poor soul is paying good money for it. The fact that you clearly do not have anyone at your firm that can answer this question is another worrying sign of where the industry is.

Matching an inverter is the very basics of PV design.
 
Last edited by a moderator:

Reply to Number of panels per string in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I have 18 panels in 2 strings (37.8v open circuit voltage each) to be connected to a Fox H1 inverter. The manual says the below. Is the 600v open...
Replies
3
Views
807
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
962
Hi, I opened the electrical panel of my house because I need to connect my solar inverter to the panel and got served a spaghetti of an...
Replies
0
Views
877
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
548

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock