Outspoken ... just to relay a answer to your reply regarding back tracking i read my first post as stating the regs do permit it on a water heater but i also state that i dont believe it should be applied in a domestic environment when in commercial or industrial the environment is usually more controlled and likely to remain as installed, if your playing the voltage change card this could apply to any circuit calculation you make where you enter 230v as nominal voltage, the regulations have tolerances on the caution built in to the tables to allow for these things, we are told to calculate to 230v but im 99% of the time seeing voltage in the mid 230s to mid 240s yet we still use 230v when designing a circuit.
'get out clause' Sums it up nicely for meI felt the original post was a well reasoned statement that indicated the difference between:
applying the regulations to all situations no matter the circumstances
and
considering the design of your installation and applying the regulations with consideration for safety.
Since BS7671 is the minimum standard to apply, ensuring that you install overcurrent protection to a cable would be a good thing in the main, even if there is a regulation that potentially allows a "get out clause".
Spark, that is Reg 433.3.1 that I quoted in the post DW was referring too, that is simply a repeat of the Reg and it does not state that it is related to showers, and it seems to me that people are arguing over nothing here as everyone seems to be of the firm conclusion that although the Regs are saying there may be situations where O/L protection may be omitted, no-one actually would omit it.
If this last point I have made is a correct reading of everyone's post I have to ask what was the point of the thread?
Would these include fluorescent fittings and LEDs?
Spark, that is Reg 433.3.1 that I quoted in the post DW was referring too, that is simply a repeat of the Reg and it does not state that it is related to showers, and it seems to me that people are arguing over nothing here as everyone seems to be of the firm conclusion that although the Regs are saying there may be situations where O/L protection may be omitted, no-one actually would omit it.
If this last point I have made is a correct reading of everyone's post I have to ask what was the point of the thread?
Low and Medium. 0.25Ω @ 230V = 211,600w (211.6kW) = 920A
Medium and High 0.338Ω @ 230V = 156,508w (156.5kW) = 680V
Low and High 0.292Ω @ 230V = 181,164w (181.1kW) = 787A
Low, Medium and High. 0.44Ω 230V = 120,227w (120.2kW) = 522A
Low 9.8Ω, @230V = 5340w (5.4kW).
Medium 6.75Ω @230V = 7837w (7.8kW) High 5.25Ω @230V = 10076.19w (10kW
Low 9.8Ω, @230V = 5340w (5.4kW).
Medium 6.75Ω @230V = 7837w (7.8kW) High 5.25Ω @230V = 10076.19w (10kW)
ok using your figures:
low and medium in parallel, 1/9.8 + 1/6.75 = 1/total, = 0.1 + 0.15 = 0.25, 1/0.25 = 4 ohms total.
230/4 = 57.5A , = circa 13kW
I think you should re read my post and I will edit mine as I forgot to divide 1 by the total....
That's what I said, you had forgotten to reciprocate the summation.
Are we forgetting that showers have a thermal cut out for any occasion when the elements overheat due to lack of water if the shower doesn't have a pressure switch or the breakdown and part shorting of the coils of the element....
The last shower I did was of the two element variety, and I was almost certain that on the higher power setting it just brought in the second element in parallel, as a boost so to speak, I could be wrong here, and I am not saying all showers are wired this way, I will have a look next time I install one.
I think your trying to over think this whole situe', the design of showers will have to comply to there own BS regulations and if multi-element then they will have a fail safe system to ensure overloading cannot happen, i find it strange that your set up has 3 stand alone setting each running on its own for a given KW rating, id be more incline to believe that the elements work together so full power is achieved by all element running. Ie. 7.5kw for element 1 and element 2 and 3 are 1.5kw each as an example. Your example outspoken would be inherently dangerous if it was possible for all elements to come on together... the least of your worries is a hot cable if your user is in intensive care having skin grafts done.... i see you are trying hard to see issues with my theme of the thread but all this has been debated time and time again especially by the IET and yet the regulation still exists, we shouldn't be stripping down the working of a shower here as thats for the manufacturers to ensure for safe fail safe operation and/or when things do go wrong it wont present a danger to the user other than a sudden cold shower.
for that to happen both the pressure sensor and thermal cut out would have to fail at the same time.They do, but if the Thermal gives way that could be the catalyst for the switch to fail due to overheating...
for that to happen both the pressure sensor and thermal cut out would have to fail at the same time.
can't say that I can see how overload protection for the circuit would help in that situation either tbh.
Is this not utilised in domestic situations all over the country , an unfused spur off a ring final circuit Iz only needs to be equal to or greater than 20a
I really think you're barking up the wrong tree here.You are assuming every shower has a pressure sensor for a start, and secondly this will depend on how they are all connected up, many showers have electronic controls these days, if they go ---- up then it could be a case of none of the safety devices work...
I really think you're barking up the wrong tree here.
standard shower protective devices are pressure sensor / flow sensor, over heat cut out, and pressure relief valve, or equivalent (eg an electronic control would presumably cut out if the electronic control failed) any shower without these (or at least 2 of the 3) would be a trading standards job IMO.
and shower elements will be nichrome, which have a temperature coefficient of resistance of 0.00017, so even if it's at 100degrees above it's starting temperature it will only increase the resistance by 0.17%. heating elements wouldn't be a lot of use if they were made of a material who's resistance increased that significantly as their temperature increased.
So a shower is very unlikely to operate for long while seriously over heating, and an overheating shower element won't draw any significant additional current anyway, so it's irrelevant to whether overload protection on the circuit would be required IMO.
circuit diagrams are your friend here.I am not sure that is accurate. Seems I will be investigating my shower again before I put it back together...