Evening all, can someone please settle a discussion i have been having recently with my supervisor. He says that although he would never do it, technically there is nothing wrong with running singles in pvc mini trunking. To me not only does it sound rough as hell, but I thought that because you can open mini trunking without a tool, then the cable would have to be double insulated. His argument is that you can get into bayonet fittings and whisker boxes without a tool, can you enlighten us, many thanks
 
your gaffer is right you can use singles in mini trunking. No need for tools on ceiling roses as they are normally over 2.2m high (reg 416.2.4 read the note )Mind you it is possible to gain access to most pvc trunking without key or tool 50x50 included.

Not sure what whisker boxes are though
 
Last edited:
your gaffer is right you can use singles in mini trunking. No need for tools on ceiling roses as they are normally over 2.2m high (reg 416.2.4 read the note )Mind you it is possible to gain access to most pvc trunking without key or tool 50x50 included.

Not sure what whisker boxes are though

Yep, no problem with singles as long as they then get a helping of double insulation, they are WISPA boxes and are basically plastic IP rated boxes with push on lids, usually installed externally
 
There's nothing wrong with PVC singles in PVC trunking. Tool or no tool, the PVC provides as much protection as the PVC sheath of T&E.
 

Reply to p.v.c mini trunking and singles in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi, I am wondering if any sparks out there know of a brand of 32mm deep PVC surface boxes with multiple knockouts for MT2 & MT3 ( 25mm x 16mm &...
Replies
6
Views
1K
Hi. I am planing on building a (not sure what to call it) U shaped storage solution which goes either side and above the headboard of a bed. I...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock