I’m carrying out a periodic on thursday on a property that has an old installation.
I’m testing it to 17th edition regs, so surely the entire installation will be deemed unsatisfactory - is this correct?
ie. no RCD, no MCBs (fuses), under rated tails, under rated main bonds etc....
Where does the client stand in this situation?
Thanks, Rob.
Most likely, but it will only be unsatisfactory in certain areas.
It's very important on the report to distinguish between the two.
My in laws have a c/unit approx 15 years old. No RCD's, but all ZS's are well within the limits.
I would code 4 this.
Hope this helps in any way,
Sav
Thanks, Rob.
The PDF posted by widdler gives guidance on what codes to apply but in the end it is the inspectors judgement.
It is important to remember that just because an installation is old it is not neccesarily unsafe. The 17th edition was only introduced a couple of years ago and to condemn all installations before it became the standard would be ridiculous.
Regarding the points you made....
No RCD...prior to the 17th RCD's were less widely used and as long as lack of RCD protection is not causing a safety issue (such as an external socket not protected,lack of RCD on a TT system etc) this would be a code 4 which would not result in an unsatisfactory.
Fuses rather than MCB's...semi-enclosed rewirable fuses still comply with the regulations contrary to popular belief....provided disconnection times are met and cable sizes comply this would not attract a code.
I'ts also worth saying that the inspector should be careful not to bring personal preferences and dislikes into his report,stick to coding only deviations from Bs 7671......and yes a PIR report is a legally accountable document so you have to be able to justify any recommendations you make...(or dont make).
Please dont think im being funny if this question comes over the wrong way, but I have heard of this before and have always been under the impression that a PIR is just that its simply the inspectors report on an installation at that particular time, not only that if two electricians inspect a property you will get two different reports. So how could it be a legally accountable document.
As I understand it if you knowingly misrepresent an installation in a PIR report in order to gain unjustified work you can be held accountable in a court of law. Likewise if following a PIR report there was a serious electrical accident or fire the report may be used as evidence......that is my understanding , if I'm wrong I stand corrected.
Reply to Periodic Inspections in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...