When carrying out the tests: live polarity of the supply, Ze, and PFC on a TN-s single phase system, what happens to the double pole main switch? is it off or on?

Many Thanks.
 
Personally I have the main switch open/off.

When I test for Ze I reconnect the earth and then test PSCC/PEFC to get the PSCC and the test polarity on the load side to make sure all is ok, and as I'm a sad git I then activate the board and test polarity on the load side of the switch
 
I am still unsure!! So the main switch off and the test is carried out at the incoming (supply) side and not the feed? OR at the feed (outgoing) side?

Many thanks.
 
With the main switch off, use the live terminal on the incoming side of the main switch and the (disconnected) main incoming earth to do your Ze. If you get a reading then you have also confirmed polarity of supply, because if polarity is wrong your tester will not do the test due to there being insufficient voltage between the 'Line' and Earth.

Sent from my HTC Sensation using Tapatalk
 

Reply to Question regarding PFC, Ze, and live polarity tests. Please help. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
740
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock