Testing some new cabinets today which had in them a PDU with a 30mA rcd upfront as main switch. ( We build among other stuff, communications cabinets for highways, railways, etc). First one tested tripped on 1/2 fault current. Tried another cab, same thing. Did a ramp test, (tester is Kewtech kt64), tripped at indicated 18mA, though it felt like it was going at 15mA, but the tester indicated 18 before it stopped. ( I think they test too fast for accurate diagnostics?) I would expect a 30mA RCD to hold until about 21-24, from experience, and would have been disappointed with 18, but for 11 to fail at 1/2? One the one hand, I hope I've missed something ever so simple so that we can ship these cabs tomorrow, but I think I've covered everything. Any thoughts?
 
Did you test at the RCD with no appliances connected? If they are ramping at 18mA then your tester might need calibrating as at 1/2 times it should be outputting 15mA.
 
Just a thought , was the test carried out with all loads disconnected/ isolated ? , could be some leakage in the equipment connected ..
 
might be some leakage on the load, as sintra said, can you test with no load connected?
 
Tested with probes, ( there's something not right about the word "probes"!) at RCD load side, tried another tester, same make, 2 years younger, tried a different test supply circuit, tried swearing at it, a lot, ( that usually works). They're A type , in anticipation of a rectifier being fitted by the client, but that shouldn't affect the test. The way I see it is no matter what the circumstances of the test, whether it's a simulated situation or real, it shouldn't trip at 1/2, it should trip at x1 and x5. Trip times for x1 and x5 were the same if that's any use? Shouldn't be too bothered as I've had enough of running a workshop and am going back into the field ( got a job as a scarecrow!), but strangely I care what leaves the 'shop whilst I'm there.
 
Although you have tested with probes , was the load completely disconnected , i.e. was the neutral and live to the load disconnected ,
 
Admittedly, no, there was still an IEC dis strip connected. The only load there in theory is a neon indicator. I'll re-test when I get in early tomorrow. Thanks for all the ideas, sleep well chaps!
 
Testing some new cabinets today which had in them a PDU with a 30mA rcd upfront as main switch. ( We build among other stuff, communications cabinets for highways, railways, etc). First one tested tripped on 1/2 fault current. Tried another cab, same thing. Did a ramp test, (tester is Kewtech kt64), tripped at indicated 18mA, though it felt like it was going at 15mA, but the tester indicated 18 before it stopped. ( I think they test too fast for accurate diagnostics?) I would expect a 30mA RCD to hold until about 21-24, from experience, and would have been disappointed with 18, but for 11 to fail at 1/2? One the one hand, I hope I've missed something ever so simple so that we can ship these cabs tomorrow, but I think I've covered everything. Any thoughts?
27-27.5 is typical for a healthy 30mA RCD

- - - Updated - - -

Is your tester set to 30mA?

A work colleague had his set to 10mA and was wondering why it didnt trip XD
your kidding....
 
They're A type , in anticipation of a rectifier being fitted by the client, but that shouldn't affect the test.

Just to check, on the KT64, on the RCD position, that you've selected "A" from the soft key, rather than "AC", otherwise you won't get the right results.
 
Thanks again for all the above;hopefully tester definitely set up correctly, as I was showing the newbie how to set it up! RCD is a Schrack 40/2/003-A
 
If the isolation of all equipment shows a correct test reading , I would then assume that you if you have computer equipment involved there is leakage from each piece , I would then look at the idea of separating the equipment to RCBOs , Another point you would have to consider is what these cabinets are being connected to when on site, I have connected PDA cabinets in the past and usually on their own circuit Identified as having high earth leakage currents , and the necessary precautions applied..
 

Reply to RCD tripping at 1/2 test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
Replies
20
Views
4K
I had a fault finding job on Thursday, intermittent RCD tripping. 2 actually, there was a 30mA RCD upstream, and a 30mA RCBO protecting the...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock