Let me see a long time since I did any testing in an industrial situation, as for a BS no what BS is the BGB? don't know try looking at it and go from there
 
Someone has just put me on the spot and asked. I have no regs book or test and inspect book on me. So was hoping for some advice to make sure I tell them the correct time scale. As we don't do much industrial. So helpful comments only please
 
If you need a reference then quote 622.1 and you can then refer to guidence note 3 table 3.2, that will satisfy them.
 
The max recommended interval for industrial given in GN3 is 3 years, however this is highly dependent on the nature and type of installation, and where other statutory/licensing regs may take precedence, or due to insurance requirements.

the interval may also be shortened or lengthened depending on what the inspector finds, also where regular maintenance schedules and records are kept then it may not be required at all.

Some factories do (a different) 20% per year, so over 5 years everything is covered.

There is no BS as such.
 

Reply to Recommended periodic testing on factories in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Hi Guys, looking at doing Initial and Periodic inspecting and testing. Looking between the CandG and EAL Just wondering if I can ask peoples...
Replies
16
Views
664
Hi I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back...
Replies
7
Views
885
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
542
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock