This may be a newbies question but the older and wiser (or at least the more experienced) heads out there may be able to help....

Just inspected a clients house and amongst the, many, problems it only has a 6mm Main Earthing Conductor. I intend to upgrade it to 16mm but I can't see how to access the earth connector in the supplier's service head. Do I really need to contact the DNO to upgrade an earth? This seems excessive and possibly expensive.
 
The earth cable from the DNO head to the main earth terminal is the DNOs property and should not be changed by you.
You could ring the DNO and say that their earthing conductor is not suitable for the load but I would check this carefully with the adiabatic equation before you ring other wise you would be charged .
 
Thanks Richard, that's confirmed what I thought, I'll go back and check the sums but I'm pretty sure that they are correct. It does make it potentially an expensive bit of cable though.
 
Just so you know. Underneath the main fuse, is a flat head screw undo that until you can slide the cover to the right. There will be the earth connections.
 
Sorry Engineer54, but making the assumtion that it is TN-C-S just because the earth conductor enters the head is not really enough.
Many heads require that a link be connected inside the head to connect the neutral and earth.
It may be that this is a conversion that took place when 6mm² was the requirement, or may be that it is a TN-S system where 6mm² is still the correct CSA.
 
Have you measured the ZE? That's what the DNO will do and if they find the reading to be acceptable then they will say its OK.
 

Reply to Replacing Main Earthing Conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
7K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock