Discuss Rewiring flat with concrete everywhere. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
12
Hi Iv been asked to price a rewire in a 9th floor flat with cast concrete walls floors and ceilings the customer is adamant they wont have trunking or lower the ceiling's, putting coving up also wouldn't work due to there being to many obstacles.

It is currently wired in pyro chased into the concrete.

Im thinking chase round high level then drop down to each point, but what about the center lights can you chase the concrete ceiling and fit conduit? or would I need to have it assessed by a structural surveyor.
 
I know this is not answering your question but this might be one of those situations in which MI pays for itself. I would be looking to re-use as much existing cable as possible and making new additions and replacements in MI too, to minimise chasing.
 
Hi Iv been asked to price a rewire in a 9th floor flat with cast concrete walls floors and ceilings the customer is adamant they wont have trunking or lower the ceiling's, putting coving up also wouldn't work due to there being to many obstacles.

It is currently wired in pyro chased into the concrete.

Im thinking chase round high level then drop down to each point, but what about the center lights can you chase the concrete ceiling and fit conduit? or would I need to have it assessed by a structural surveyor.
I would personally give it a wide berth. Once worked in a tower block changing singles to doubles and the noise that's made chasing walls had neighbours from up and down complaining, not worth the hastle.
 
Unless you're very competent with M.I,, Pyro,, then don't even think about it otherwise you'll have to pay someone else to do it.

It's unlikely you'll be able to chase the ceiling for structural reasons and more importantly as above the noise.
The M.I is most likely fixed on top of the concrete then plastered over it won't be chased.
It could also be singles in steel conduit embeded in the concrete

Before you quote, if you do, you need the customer to speak to the neighbours above, below and at the sides and get written agreement about the noise, otherwise you could end up being stopped half way through it all and it'll get messy re getting paid.
 
Thanks for the advise good point about the noise complaints, I think battening the ceiling would be the sensible option bit don't think the customer will do for it il put that to them and see what the response is.
I sometimes spend hours doing research quotes etc... knowing the customer 8s going to say no. Don’t know why I do it.
I think this may be the case with this job for you.
good luck, but if your not short on work I’d limit your valuable time with this one until they compromise.
 
The concrete reinforcement in ceilings, floors and walls are at a specific depth to transfer the stress of the structure into the surrounding concrete its called d1 in structural terms decreasing that depth over any distance is reducing the integrity of the structural member, in other words DON'T DO IT, the existing cable or conduit will not be in the structural zone or calculated depth of the structure so could be safely used again.
 
Fixed with double sided tape so you don't drill into the concrete, ? And don't forget to make the conduit a feature by painting it bright red.?
 

Reply to Rewiring flat with concrete everywhere. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Some advice please as I think that the flat below mine is being rewired by someone who isn’t qualified. The small basement flat below...
Replies
24
Views
3K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K
Looking at a job tomorrow evening for a new 5 bed house +granny flat over a basement floor+ground. In my initial phone call to the client-...
Replies
22
Views
2K
Squid
S
Z
Has anyone come across this problem and is there any way around it other than pulling down the ceilings ? first floor flat, concrete floor...
Replies
20
Views
9K
P
Morning gents, New to the site! Looking for a little advice from the old boys on how to tackle this job. We were asked to quote a job in North...
Replies
8
Views
993

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock