I would use 2 core 25mm swa and a separate 16mm earth. Terminated in a metal clad box (or plastic with 32mm knockouts) feed it from a 100A main switch there to an adaptable box (again with 32mm knockouts. And then supply your board as normal with meter tails from the adaptable box.

Or use 3 core swa and leave one core a bit longer so it will go from the earth at source (tns) to a met at the db. Would look something like this in the end.

9yvevy5a.jpg
 
As it's TN-S you don't need to do ^^^. The Cu Equiv. of the armour should more than meet your adiabatic.
 
I would use 2 core 25mm swa and a separate 16mm earth. Terminated in a metal clad box (or plastic with 32mm knockouts) feed it from a 100A main switch there to an adaptable box (again with 32mm knockouts. And then supply your board as normal with meter tails from the adaptable box.

Or use 3 core swa and leave one core a bit longer so it will go from the earth at source (tns) to a met at the db. Would look something like this in the end.

9yvevy5a.jpg

No overload protection for the sub main then?
 

Reply to Service point in out building in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
572
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
544
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock