Hi there.
My friend is building a new house. He has decided to put service point in and out building next to new house. A duct has been run from out building to house. I will be using 16mm three core to supply house db. I've decided to use rcbo's for circuits in the house. But I am unsure if the cable at the out building side should be rcd after the cut off to supply the house? Any advice would be appreciated.
 
Two things:

1) Check your calculations for voltage drop for the lighting - you might need to upgrade that 16mm to a 25mm depending on length of run
2) It would probably pay you to bring the incomer into a metal-clad consumer unit anyway as that way you have something to make your armoured off to and also can run some ancillary sockets and lights in the outhouse more easily.

No, you don't need to provide upstream RCD protection to the cable, but personally I would install it onto a DP MCB rather than a single.
 
1 and 1/2 storeys? must be DIY as he's already demolished half the upstairs. :drool5:
 
The half storey is built in the roof space with dormers!!!

sounds like some sort of hobbit hole..........


hobbit.png

what the hell are you building over there ? lol.

;-)
 
MP: Shoe box?
TG: Aye.
MP: You were lucky. We lived for three months in a brown paper bag in a septic tank. We used to have to get up at six o'clock in the morning, clean the bag, eat a crust of stale bread, go to work down mill for fourteen hours a day week in-week out. When we got home, out Dad would thrash us to sleep with his belt!
GC: Luxury. We used to have to get out of the lake at three o'clock in the morning, clean the lake, eat a handful of hot gravel, go to work at the mill every day for tuppence a month, come home, and Dad would beat us around the head and neck with a broken bottle, if we were LUCKY!
 
I would use 2 core 25mm swa and a separate 16mm earth. Terminated in a metal clad box (or plastic with 32mm knockouts) feed it from a 100A main switch there to an adaptable box (again with 32mm knockouts. And then supply your board as normal with meter tails from the adaptable box.

Or use 3 core swa and leave one core a bit longer so it will go from the earth at source (tns) to a met at the db. Would look something like this in the end.

9yvevy5a.jpg
 
As it's TN-S you don't need to do ^^^. The Cu Equiv. of the armour should more than meet your adiabatic.
 
I would use 2 core 25mm swa and a separate 16mm earth. Terminated in a metal clad box (or plastic with 32mm knockouts) feed it from a 100A main switch there to an adaptable box (again with 32mm knockouts. And then supply your board as normal with meter tails from the adaptable box.

Or use 3 core swa and leave one core a bit longer so it will go from the earth at source (tns) to a met at the db. Would look something like this in the end.

9yvevy5a.jpg

No overload protection for the sub main then?
 

Reply to Service point in out building in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
618
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
593
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top