Discuss Size of shower cable in the UK Electrical Forum area at ElectriciansForums.net
B
Bensen
Hey what kilowatt showers can be feed off 6mm cable and which need 10mm? I guess the distance from the fuse board also needs taking in to account?
Hi Bensen, distance plays a big part along with other factors including overcurrent protection and installation methods. I see from your profile that you are a plumber so IMO you should leave electrical cable calcs to the sparks.
Thanks would many sparks also do the plumbing on an electric shower. Its a swap or a 25year old plus electric shower that has stopped working.
considering the last plumber that i last had fit the water supply to a shower... brought it out 2 ft. below where i'd marked the studded wall, so the shower unit would have been only 2ft. above the bath and the cable 2 ft. above the shower, i do my own shower pipework now.
Each shower install would need to be assessed and designed on an individual basis and in accordance with appendix 4 of the regs. The kW rating of the shower and cable length are just 2 of many factors involved. This is definitely a job for someone who has been properly trained in circuit design.
Very broadly speaking up to 8.5kw on a 6mm
8.5kw to 10kw will need a 10mm
You need to consider some very important variables including,
The installation method ie is the cable run enclosed in some way or clipped direct.
Is the cable running within some form of insulation ect.
To explain,
The cable under load generates temperatures above ambient, and its ability to dissipate those temperatures will be greatly affected by the way its installed.
You also have to consider the length of run as this can affect the difference between the supply voltage at source and the voltage at the load/shower terminals.
This is known as volt drop and directly relates to the internal resistance of the cable per metre, in relation to its cross sectional area.
The characteristics of the protective device are also important as you need to ensure that the device disconnects the supply before the user of the shower receives an electric shock, should a fault condition develop.
The installations integrity need to be verified to ensure insulation,polarity, along with a low resistance earth return path are able to satisfy these requirements.
A certificate recording these results is produced to provide a paper trail for future reference.
Building regulations under part P also come into play when working in bathrooms as they are known as a special location, and these are divided into various zones for compliance.
If all this makes sense to you and you have the appropriate test equipment and knowledge to use it, then your good to go.
If not, consult a qualified electrician.:icon12:
To explain,
You have just given this plumber a green light IMO lol
To explain,
Stuff and nonsence :biggrin:
New posts
Reply to Size of shower cable in the UK Electrical Forum area at ElectriciansForums.net
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
hi ive got an unused isolator in my airing cupboard that use to run a shower. no longer have has have combi boiler feeding a new shower. the...
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...