B
Bensen
Hey what kilowatt showers can be feed off 6mm cable and which need 10mm? I guess the distance from the fuse board also needs taking in to account?
Discuss Size of shower cable in the UK Electrical Forum area at ElectriciansForums.net
Meh, it's only a few wires man. What can possibly go wrong?
Apart from a horrible, painful, fiery death.
Of course mate. How foolish of meunless of course you fit a steel DB.
Hey what kilowatt showers can be feed off 6mm cable and which need 10mm? I guess the distance from the fuse board also needs taking in to account?
Very broadly speaking up to 8.5kw on a 6mm
8.5kw to 10kw will need a 10mm
You need to consider some very important variables including,
The installation method ie is the cable run enclosed in some way or clipped direct.
Is the cable running within some form of insulation ect.
To explain,
The cable under load generates temperatures above ambient, and its ability to dissipate those temperatures will be greatly affected by the way its installed.
You also have to consider the length of run as this can affect the difference between the supply voltage at source and the voltage at the load/shower terminals.
This is known as volt drop and directly relates to the internal resistance of the cable per metre, in relation to its cross sectional area.
The characteristics of the protective device are also important as you need to ensure that the device disconnects the supply before the user of the shower receives an electric shock, should a fault condition develop.
The installations integrity need to be verified to ensure insulation,polarity, along with a low resistance earth return path are able to satisfy these requirements.
A certificate recording these results is produced to provide a paper trail for future reference.
Building regulations under part P also come into play when working in bathrooms as they are known as a special location, and these are divided into various zones for compliance.
If all this makes sense to you and you have the appropriate test equipment and knowledge to use it, then your good to go.
If not, consult a qualified electrician.:icon12:
Thanks would many sparkys be able to take care of the plumbing too. Its an old 25year plus shower that needs swapping.
Yes please, I also like Mustard.Hey what kilowatt showers can be feed off 6mm cable and which need 10mm? I guess the distance from the fuse board also needs taking in to account?
Stuff and nonsence :biggrin:Very broadly speaking up to 8.5kw on a 6mm
8.5kw to 10kw will need a 10mm
You need to consider some very important variables including,
The installation method ie is the cable run enclosed in some way or clipped direct.
Is the cable running within some form of insulation ect.
To explain,
The cable under load generates temperatures above ambient, and its ability to dissipate those temperatures will be greatly affected by the way its installed.
You also have to consider the length of run as this can affect the difference between the supply voltage at source and the voltage at the load/shower terminals.
This is known as volt drop and directly relates to the internal resistance of the cable per metre, in relation to its cross sectional area.
The characteristics of the protective device are also important as you need to ensure that the device disconnects the supply before the user of the shower receives an electric shock, should a fault condition develop.
The installations integrity need to be verified to ensure insulation,polarity, along with a low resistance earth return path are able to satisfy these requirements.
A certificate recording these results is produced to provide a paper trail for future reference.
Building regulations under part P also come into play when working in bathrooms as they are known as a special location, and these are divided into various zones for compliance.
If all this makes sense to you and you have the appropriate test equipment and knowledge to use it, then your good to go.
If not, consult a qualified electrician.:icon12:
coming from someone who likes creamflow,:ack2:, that's not a very good advert for colmans.Yes please, I also like Mustard.
Afternoon Terence :biggrin:coming from someone who likes creamflow,:ack2:, that's not a very good advert for colmans.
Hi Bensen, distance plays a big part along with other factors including overcurrent protection and installation methods. I see from your profile that you are a plumber so IMO you should leave electrical cable calcs to the sparks.
I'm sayin' nowt!! :uhoh2::38:
coming from someone who likes creamflow,:ack2:, that's not a very good advert for colmans.
well, that's a first!
Reply to Size of shower cable in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.