Discuss Supplier earth terminal on intake in the UK Electrical Forum area at ElectriciansForums.net
From the two DNO's in the areas I work the shrink kit and braid earth is ENWL's solution which is quite neat and tidy while SP Energy Networks use something similar to a "jubilee" clamp around the PILC for the earth with a 6491x 16mm earth cable connected to it and a sheet rubber self adhesive wrap around it which looks quite bulky and a bit rough
I've never been a fan of jubilees on lead, always makes me nervous. The good thing about enwl kit Is that it's not tight pressure to the lead but it's more than enough to create a good and secure bond, especially with the mesh around the lead and the braid tied into it before the roll springs are applied. I've worked across multiple dnos over the years and find enw to have the best jointing techniques and terminations compared to other DNO's
Update to original post.
SSE attended earlier this week. I wasn't there and initially they said the connection was fine, it was a PME supply. The customer had to insist it wasn't, so they opened it up, muttered something about the earth being in the wrong terminal, and reconnected it per the updated photo.
Ze now measured 0.23 Ohm.
Perhaps needs a warning label that the "earth" terminal is not actually earthed?
But that makes sense and would cost a couple of pence, not going to happen.
How about a label to indicate it is now a PME supply
Does the earth cable connect to a separate earth block now
Yes, a PME label would also be helpful.
The earth cable connects to an earth block nearby, with gas & water bonding & earthing for the consumer unit.
Reply to Supplier earth terminal on intake in the UK Electrical Forum area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...