Hi whilst doing the split method insulation resistance test.
After opening the mid point socket,whilst putting 500v through one of the legs are you supposed to leave the other end in the mcb and if not do u terminate it?
 
Depends on how you have acheived safe isolation, been an mcb the IR test will not damage it but the issue is that it is turned on making open ends live, if you are trying to split the 2 halfs of the ring at the fuseboard to the midpoint then they need disconnecting from the mcb and N bar anyway and ends making safe for the testing. (leaving the N connected globally could see false readings from other circuits or a dead S/C between E/N if main switch is still on due to the supply TX where you may have only disconnected at the mcb.
 
Last edited by a moderator:
  • Like
Reactions: 1 person
You effectively need to turn the ring into 2 seperate radials and then test each one to find which half the fault is on, you split the cores in the CU and also split them at the midpoint or as near to as possible, as you cannot be at both ends during the test then just pop the ends seperately into some connectors to ensure no-one will get a zap from your insulation tester.
 
Last edited by a moderator:
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Testing
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Wilson12,
Last reply from
Darkwood,
Replies
3
Views
123

Advert