Discuss Think I must be confused! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
mhar
An underground tt supply going into a meter cabinet on the outside of a garage, 16mm tails straight through the wall to henley blocks, 10mm earthing conductor to a rod with a Ze of 38ohms. From henley blocks a small gagage sub main with a 63A 100ma T rcd, main house feed from henley blocks (in 16/16/16 split concentric cable) back into the meter cabinet and through underground ducting feeding house cu where circuits are protected by 2 x 80A 40mA. House built approx 1980.
Asked about this at school yesterday where I was lent gn8. From my reading there could be two issues.
1) Lack of a 100mA T rcd protecting the house feed and
2) The house feed needs a cpc but this should not be connected (house cu end), instead a separate earth electrode should be provided.
So my confusion is that the logical, practical and most convenient place for this new rod is back through the ducting to roughly where the existing rod is but only in 10mm. Surely it makes sense to keep the existing 16mm earth rather than replace it with a 10mm one.
Am I misreading something? Don't worry, I am not the person doing this, just trying to learn!
If the house CU is more than 3 meters away from the main fuse then there needs to be an overcurrent protection as well as an RCD. Also the 1st enclosure (where the RCD is) should not be metal - class II.
Can't see a problem with the earth to the house CU if I understand what you're saying.
Heley blocks to 80A fused isolator and then split con to house. The garage rcd only protects the garage submain.
Gn8 clearly shows the cpc running alongside the feed but not connected at the house end but a separate electrode being used. Two different equipotential zones I assumed
Reply to Think I must be confused! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
5K
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...